Results 1 to 2 of 2

Thread: Gas fire pit

  1. #1
    June O'Leary's Avatar
    June O'Leary Guest

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Gas fire pit

    If the gas fire pit is a listed unit, it should state the distance in the installation instructions.

    If the gas fire pit is not a listed unit ... it is required to be a listed unit, so don't install it.

    If it is is not a listed unit and you install it anyway - WHICH YOU SHOULD NOT DO - install it at least as far away as unlisted open flame items, such as Hibachi grills and other similar grills and devices for charcoal/wood/etc ... the minimum clearance for those units is 10 feet from any part of any structure - BUT ... it should be a listed unit or do not install it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com