Results 1 to 8 of 8
  1. #1
    Brian Egan's Avatar
    Brian Egan Guest

    Default Venting gas furnace in attic

    I need to vent a gas furnace 83% non condensing through pitched roof. Furnace connection is 4" dia with draft inducer motor. Furnace is located in attic with connection 30" below and 18" offset from roof peak. A) Must I use B vent? B) How high should the penetration through roof be" C) Is B vent rain cap suitable? Appreciate any input. Thank You Brian

    Similar Threads:
    Crawl Space Creeper

  2. #2
    David Bell's Avatar
    David Bell Guest

    Default Re: Venting gas furnace in attic

    B-vent though the roof with termination 1 foot above the peak.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Venting gas furnace in attic

    Quote Originally Posted by David Bell View Post
    B-vent though the roof with termination 1 foot above the peak.
    Is it allowed to use B vent with a draft inducer motor? I thought B vent was not allowed to be used with a pressurized venting system, and doesn't the draft inducer motor pressurize the venting system to some extent?

    I'm asking because I do not know, I have not seen that done before (mostly electric around here).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    David Bell's Avatar
    David Bell Guest

    Default Re: Venting gas furnace in attic

    The venting of an 83% draft induced furnace is typically done with single wall pipe to a b-vent thru the roof. No different than natural draft.


  5. #5
    Join Date
    Jul 2009
    Location
    Virginia Beach
    Posts
    25

    Default Re: Venting gas furnace in attic

    Use B-Vent with listed B-Vent cap. The termination height depends on the roof pitch, and is at least 12" and increases as roof pitch increases. The B-Vent is acceptable because Category I fan-assisted appliances deliver flue products to the vent with neutral or negative pressure. Check apliance installation manual for other requirements, especially minimum vent height since the outlet is fairly close to the roof.


  6. #6
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: Venting gas furnace in attic

    An 83% fan assisted furnace is CAT I, which is approved for B-vent. In fact, since it is an attic, you must use B-vent. However, you also need to refer to the appliance's listed instructions for minimum vent height, which usually starts at 5 ft. If the appliance collar is only 30" under the roof deck, you'll need to extend the vent above the roof at least 18" plus any requirement for vent height per the roof pitch.

    if the vent extends 5ft or more above the roof, you would need roof brackets to stabilize and support it. You also would need to figure how you are going to support and stabilize the vent so it doesn't wobble around.

    Keep the fire in the fireplace.

  7. #7
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Thumbs down Re: Venting gas furnace in attic

    Not my best hour of the day...or rather night (!); but this is a gas furnace, in the attic, right?

    I'm thinking there is also prescribed rule regarding minimum developed height/rise that also requires a minimum of 10 feet from the bottom of the furnace appliance to the vent outlet? (not just a five foot rule?) or more as the manufacturer's instructions and listing may require further.

    I'm with Bob H. that, you may not use a single wall vent connector to an appliance's flue collar or draft hood, which is located in the attic.

    What's the make up, combustion & dilution air source, is the attic an open one? is it conditioned? finished?

    I might have missed something. Up late and detoured as the bucket of halloween candy called out to me as I was heading back to bed.


  8. #8
    Join Date
    Feb 2009
    Location
    Southeast Virginia, Hampton roads
    Posts
    51

    Default Re: Venting gas furnace in attic

    Hmmm...there's some pretty informed inspectors here, but this is an inspection forum. You may want to try a gas fitter qualified HVAC contractor.

    When "functional" is not good enough, Call Final Analysis Home Inspections, Virginia Beach VA