    Default three wire to storage shed
    I just wanted to check real quick on the rule on regular 3 wire romex being feed from the house to a storage shed in back yard. not outdoor wire either, pretty wrong in my book but wanted to know the rule on the certain kind of wire. Thanks
    E.D.S
    Home Inspections
    Lic.#450.010534
    Default Re: three wire to storage shed
    Regular NM or NM-B is not for use in wet or damp areas. You can find both the acceptable and prohibited uses in Article 334 of the NEC.
    Mar 2011
    Virginia Beach, VA
    Eric,
    Apart from the very obvious issue that NM/NMB is not to be used underground, there can be further problems if this is a three wire feeder from a panelboard to another panelboard, they a 4 wire cable is required.
    Also, the depth of the cable trench can be an issue. Not to mention, if they are bringing power to the 2nd. building, then they must put a light outside near the entry way into the building.
    Quote Originally Posted by Donald Farrell View Post
    Eric,
    Hi Donald,
    Who "must" put a light outside......?
    Corey
    Eric,
    Quote Originally Posted by Corey Friedman View Post
    Hi Donald,
    Corey
    Whomever is in charge.
    As required by the IRC and NEC.
    Wink Re: three wire to storage shed
    Hi Jerry,
    As you know, in a private real estate transaction the only "must" (for something like this) is what the two parties agree to, which can range from everything to nothing.
    Be well,
    Corey
    Hi Jerry,
    Be well,
    Corey
    Corey,
    I suspect that Donald was referring to when the house is constructed, not to the current real estate transaction where the home inspector is pointing out what was not done when it should have been done.