Results 1 to 7 of 7
  1. #1
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Question RE: Grounding

    I have a Service equipment panel located roughly 10 feet from the first remote panel.
    My question is; the GEC are located on the opposite side of the garage remote panel and actually run into the remote as pictured, which actually looks like a service panel.(There's other stuff wrong in there I know, but for now just concerned about the grounding)
    So I'm confused...shouldn't the garage aux panel be separated like an aux panel should be in this case? Or, is it okay to connect the GEC in this panel like a service panel. Gut tells me no but willing to get schooled.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Charlotte NC Licensed in NC and SC
    Posts
    597

    Default Re: Question RE: Grounding

    I can't comment on the pictures but basically the GEC must go to the main panel unspliced. Then the load panel would be typical, 4 wire feed with neutrals floating off ground. Sometimes you will find two main panels so then both would have a GEC that can be seperate or one jumped off the other.

    Bruce King, B.A. King Home Inspections, LLC
    www.BAKingHomeInspections.com
    Certified Master Inspector, Independent Inspectorwww.IndependentInspectors.org

  3. #3
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: Question RE: Grounding

    The GEC should be connected to the main (first) disconnect, or before (meter or similar). All GEC connections should be made at the same place. It is not permissible to use an equipment ground at a non-service panel in the same structure to make a GEC connection.

    GECs serve a completely separate function from an equipment ground and those functions aren't allowed to share conductors.

    Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.

  4. #4
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Question RE: Grounding

    Got it. I appreciate the information.
    Marc


  5. #5
    Join Date
    Feb 2009
    Location
    On The Mason-Dixon Line
    Posts
    577

    Default Re: Question RE: Grounding

    Quote Originally Posted by Bruce King View Post
    I can't comment on the pictures but basically the GEC must go to the main panel unspliced. Then the load panel would be typical, 4 wire feed with neutrals floating off ground. Sometimes you will find two main panels so then both would have a GEC that can be seperate or one jumped off the other.
    One small correction. The GEC can be spliced, BUT it must be an irreversable splice such as crimped or exothermic weld.


  6. #6
    Join Date
    Mar 2007
    Location
    Chicago
    Posts
    164

    Talking Re: Question RE: Grounding

    "I have a Service equipment panel located roughly 10 feet from the first remote panel."

    Ok, just gotta ask. What is a "remote" panel? Does that mean a panel operated by remote control like my TV remote or a different location like a submarine? Just kiddin'.....

    Happy holidays to all.

    Corey

    Last edited by Corey Friedman; 12-20-2011 at 03:05 PM. Reason: quoted wrong post

  7. #7
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Question RE: Grounding

    Quote Originally Posted by Corey Friedman View Post
    "I have a Service equipment panel located roughly 10 feet from the first remote panel."

    Ok, just gotta ask. What is a "remote" panel? Does that mean a panel operated by remote control like my TV remote or a different location like a submarine? Just kiddin'.....

    Happy holidays to all.

    Corey
    LOL...cant win in here. Remote, sub, auxiliary..."other" panel..


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •