    Last edited by Clay E White; 01-04-2008 at 02:33 PM.
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: Water HEater Vent

    Should be properly supported when it changes direction.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  3. #3
    Join Date
    Mar 2007
    Location
    Kalamazoo, MI
    Posts
    117

    Default Re: Water HEater Vent

    Clearance to combustibles on single walled vent pipes should be 3in and on double walled (B-Vents) should be a min of 1in. Looks like the vent pipe does not meet this.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Water HEater Vent

    Quote Originally Posted by Robert Dalga View Post
    Clearance to combustibles on single walled vent pipes should be 3in
    I believe that is 6 inches for single wall vent.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired