Results 1 to 3 of 3
  1. #1
    Join Date
    Mar 2007
    Location
    Colorado Springs, CO
    Posts
    1,217

    Default Plumbing Vent Roof Jack At Valley

    Ordinarily I would blame a lazy or inattentive plumber for placing a plumbing vent so close to a roof valley. But in this case this was an existing vent that years later ended up too close to a valley that was created when a rear addition was built.

    Anyway, the valley flashing was stepped and notched to accomodate the roof jack flashing. Does anyone see a problem with the flashing for the roof jack encroaching into the valley? What comments would you make?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral
    "Baseball is like church. Many attend but few understand." Leo Durocher
    Bruce Breedlove
    www.avaloninspection.com

  2. #2
    David Banks's Avatar
    David Banks Guest

    Default Re: Plumbing Vent Roof Jack At Valley

    Bruce. I got this from Inspection News a while back. Just change chimney.

    CHIMNEY IN VALLEY:
    : There is supposed to be a 36" wide moisture barrier underlayment at all valleys, 18" to either side if installed correctly, Therefore no chimney(s), plumbing vent(s), or flue stack(s) should be placed within 18" of a valley. Penetrations to the moisture barrier may eventually leak and these areas will require further monitoring and sealant application if not relocated and installed correctly.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Plumbing Vent Roof Jack At Valley

    We went through this recently, and it depends on how valleys are done in your area. (That's what was decided here.)

    Many areas install a 16" wide valley metal in the valley, which extend out from the center 8" to each side, stay outside that valley metal and there is no problem.

    Other areas install a 36" wide roll down the center of the valley, which extends out 18" ...

    I'm not sure that the flashing in your photo is even 8" out from the center of the valley, and that is the minimum distance to clear the valley metal.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •