    I can't find anything on GE's web site or anything in NEC backing up my thoughts that this SE is improperly installed. I know the builder is going to want to argue this point I made. Please point me in the right direction. Thanks in advance.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    john thurmond's Avatar
    john thurmond Guest

    Smile Re: Surface Mounted SE Recessed

    Sorry, It's an all in one GE CTL Surface Type 3R


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Surface Mounted SE Recessed

    (underlining is mine)
    312.2 Damp, Wet, or Hazardous (Classified) Locations.
    - (A) Damp and Wet Locations. In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6-mm (ΒΌ-in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof. For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations.
    Exception: Nonmetallic enclosures shall be permitted to be installed without the airspace on a concrete, masonry, tile, or similar surface.
    FPN: For protection against corrosion, see 300.6.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    john thurmond's Avatar
    john thurmond Guest

    Thumbs up Re: Surface Mounted SE Recessed

    Jerry, thank you for your quick response. Builders here are rushing the electrical install before hard coat or EIFS is completed and it's my person quest to let them know about it. I knew I had read that they must be able to drain behind the panel so they don't rust-out etc. On behalf of all the other mostly silent readers of this MB, your expertise is always appreiciated. Thanks agian, JT


  5. #5
    Join Date
    Mar 2007
    Location
    South-West Michigan
    Posts
    469

    Smile Re: Surface Mounted SE Recessed

    I don't bother to argue with builders. I ask them for their supporting documentation in printed form. They go away.

    Randall Aldering GHI BAOM MSM
    Housesmithe Inspection
    www.housesmithe.com

  6. #6
    Aaron Miller's Avatar
    Aaron Miller Guest

    Wink Re: Surface Mounted SE Recessed

    John:

    I think you might want to add that the stucco installation is also incorrect as regards termination at a dissimilar material. The system must be properly spaced and then sealed with a low modulus sealant approved by the manufaturer.

    Aaron


  7. #7
    john thurmond's Avatar
    john thurmond Guest

    Talking Re: Surface Mounted SE Recessed

    Aaron:
    I did address the stucco concerns. I even found out the mfg and application details were Unicoat for the hardcoat and Drivit for the finished coat. I just reported what I saw, the builder agreed to give home buyer a 5 year warranty on the stucco after a few other repairs were made. I replied to the home owner that her house may not be there in 5 years... See fireplace termination cap... LOL I had addressed the location of the vent termination at the pre-drywall/framing inspection. He(builder) didn't move it then, and now it's gonna be expensive to move. County Inspector never said a word about it.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  8. #8
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Surface Mounted SE Recessed

    John, that does indeed look too close to the side wall to me.
    Do you know the clearance requirements for that unit?

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  9. #9
    Aaron Miller's Avatar
    Aaron Miller Guest

    Default Re: Surface Mounted SE Recessed

    Quote Originally Posted by john thurmond View Post
    Aaron:
    I did address the stucco concerns. I even found out the mfg and application details were Unicoat for the hardcoat and Drivit for the finished coat. I just reported what I saw, the builder agreed to give home buyer a 5 year warranty on the stucco after a few other repairs were made. I replied to the home owner that her house may not be there in 5 years... See fireplace termination cap... LOL I had addressed the location of the vent termination at the pre-drywall/framing inspection. He(builder) didn't move it then, and now it's gonna be expensive to move. County Inspector never said a word about it.
    John:

    Damn fine looking work to me. And a 5-year warranty from a builder is about as valuable as it sounds . . . worthless.

    Aaron


  10. #10
    john thurmond's Avatar
    john thurmond Guest

    Default Re: Surface Mounted SE Recessed

    Good question Jim,
    The unit mfg states 6", local jurisdiction says 9", builder says that 5" that is there is acceptable. I was ready for battle but the home owner didn't want to cause a fuss with the builder. "OK Lady, it's your home..."