    Sep 2009
    Twin Cities, Minnesota
    Default Testing Ground Fault Breakers
    I use an Ideal SureTest ArcTester. I plugged it into a circuit lacking a ground but protected by a ground fault breaker and pressed the GFCI button, but the circuit breaker didn't trip. It did respond to the test button on the breaker. Do the Ideal SureTesters not trip ground fault breakers? I was able to trip other GFCI outlets in the house with the tester.
    -Jon
    Errickson Home Inspections, LLC
    http://www.erricksonhomeinspections.com
    Default Re: Testing Ground Fault Breakers
    The Ideal needs an equipment ground to test GFCI devices.
    Since the breaker tripped with its own test button, it's ok.
    Oct 2011
    Eastern Shore of MD, NEC 2008
    I believe the only UL approved method of testing GFCI devices is the test button.
    Both Derek and John are correct about the testing methods and the need for an EGC in order for the tester to trip the GFI.
    Quote Originally Posted by Derek Guridi View Post
    More specifically - GFCI and AFCI device manufacturer's will only recognize the test buttons on the device. In other words, any AFCI/GFCI tester you carry is useless for testing applications.
    I've said this before but I like saying it.
    The test button doesn't prove the circuit was wired correctly. For example, the circuit or the receptacle might still be live with the breaker tripped.
