    Aluminum wire connected to 50 amp 240 volt breaker. Breaker is labeled CU Only, but once I got home to finish the report I see the label also has CU/AL on it. How is this label to be interpreted?
    Default Re: Breaker Labling
    Confusing to say the least. However, if I were to guess I would say that CSA has only listed the breaker for use with copper. I don't know why they would list it differently than Siemens.
    Might be time for a phone call to Siemens Tech Support.
    Mar 2009
    Colorado Front Range
    The CU only is above the column for amperages 35 or under. The breaker is listed for aluminum for 40 to 50 AMPs.
    Yes, confusing. The "cheap at any inconvienience" shows up here in the form of being too cheap to make a stamp for different sizes of breakers.
    Mar 2009
    Why I have to carry copies of manufacturer's catalogs around in the "smart phone" for building inspections.
    Robert Meier's Avatar
    Robert Meier Guest
    Are these CB's feeding AC units? Otherwise the conductors look a little small.
    Don Martin's Avatar
    Don Martin Guest
    Yes, to AC units
    The wire connector screws don't look right to me. They appear to be simple slotted screws, and not combination slotted/robertson screw heads from what I can see in the first photograph of the four wire connector screw heads I can see in the first photograph in various positions. I may very well be mistaken, but I thought all residential Siemens QP breakers had combination slot/robertson wire connector screws on them.
    I'm also not recalling EVER seeing a black label on a SIEMENS QP Breaker wherein SIEMENS hasn't been in ALL Capital Letters.
    I'm also wondering why I am seeing the word "Listed" (in upper & lower case) to the right of the UL insignia & trademark lacking a US lower right of the UL insignia circle; and not below same, and how the word "Listed" has been run together with an abbreviated description. I am further concerned as to the improper proportion appearance of the CSA insignia and the lacking trademark mark which is always to the right center of the open C, as discussed in the second link whitepaper from CSA on Counterfeiting products and the improper use of their insignia marks dating back to 2002; and some other "typesetting" concerns on the labels.
    I am suspicious that the pictured may be counterfeit. Unknown age of what is pictured, and obviously more details would be necessary to explore/confirm with the manufacturer, including the breaker side view and label information (origin, date code, etc.).
    See white paper from Siemens attached. Although it focuses more on the 15 & 20 Amp QPs it does address the issue in general.
    Contact information is included in the attached. If you prefer to read the Siemens white paper from last year on line it may be viewed here: http://www.sea.siemens.com/us/intern...terfeit_WP.pdf
    CSA's whitepaper on counterfeiting anti-counterfeiting efforts, hosted on NEMA.org's website: http://www.nema.org/gov/anti-counter...te_paper_e.pdf
    Attached Files Attached Files
    Last edited by H.G. Watson, Sr.; 02-22-2012 at 11:51 PM. Reason: added link to CSA whitepaper regarding suspect mark
    Don Martin's Avatar
    Don Martin Guest
    Wink Re: Breaker Labling
    HG you are a paranoid old..... :-)
    20 year old house. I assumed the breakers are original except for one or two of the branch circuits. The house is vacant and the panel is accessible so I might just have to go back and get a few more photos. I won't be in the area tomorrow but possibly Friday.
    I'll let you know
    Chico,Ca
    Looks like the breaker is copper only for Canada, since the OP is in Bakersfield, what it is listed for in Canuckistan is irrelevent.
    Don Martin's Avatar
    Don Martin Guest
    A few more photos of the suspect breakers.
    Rollie, please explain about the Canadian listing.
    Chico,Ca
    Quote Originally Posted by Don Martin View Post
    The breaker is UL listed as shown by the photos in the orig. post, it is marked as "CU/AL 60/75°C WIRE" below it is the CSA trademark w/ "CU only" on it which means to me it a Canadian listing restriction that has no value outside of Canada.
    Thanks, Rollie. CSA - Canadian Standards Association.
    Now tell us why those breakers had to be assembled in Mexico.
    Oct 2011
    Minneapolis, MN
    Perhaps when these were made the CSA knew something UL didn't, and listed them the way they did for good reason. Just because they're in a different country doesn't make them any safer.
    - James Burgh, 1754.
    Chico,Ca
    Just like everything else, 'cause of cheaper labor...... & the North American Fraud and Theft Agreement, NAFTA that Canukistan,the US & Mexico are part of.
    The first photo in Don's followup post/series clearly confirms that the wire connector screws are simple slot-only type and that
    Combination slot/robertson wire connector screws are not present.
    Would have expected combination slot/robertson wire connector screws for January 1992 mfg and esp. for Canadian approval/market labeling.
    Suspected counterfeit, the panel as well, suspected counterfeit/bootleg.
    The hotline number and contact information for SIEMENS has already been supplied earlier. Suggest verification of authenticity or suspected counterfeit-ness with Manufacturer.