    Default breach in drain line

    Saw a condensation line that is put directly into a 2 in drain in the crawl. They drilled a hole in drain line. Hose fits tight in it but I still called it out. Would just some sealant be allowed or a proper fitting cut into the drain with a leg for it be better.

    Similar Threads:
    Inspection Referral
    E.D.S
    Home Inspections
    Lic.#450.010534

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: breach in drain line

    Quote Originally Posted by Eric Smith View Post
    Would just some sealant be allowed
    Nope.

    or a proper fitting cut into the drain with a leg for it be better.
    That would not just be 'better', that would be 'required'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: breach in drain line

    It sounds totally illegal. I visualize a condensate line tapped into a drain line... which is wrong in many ways. A little sealant or a better fitting will not make it a proper connection. It needs to be an indirect connection at a trapped standpipe or other approved method.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  4. #4
    Join Date
    Jul 2009
    Location
    Lanham, MD
    Posts
    86

    Default Re: breach in drain line

    In many jurisdictions (including mine), it is not legal to discharge condensate into the sanitary system. Condensate must be discharged to grade or to storm drain either directly or indirectly i.e. by a sump pump. So even if the connection is made using proper fittings, it still may not be allowed.