    Default Bonding jumper location on Pushmatic Bulldog panel

    Load-side panel. Labeling was not visible and I could not locate the bonding jumper location.

    Anyone know where I should be looking?

    Yes, I know panel is obsolescent - whole unit was obsolescent, furnace was a Lenox manufactured in Oct. 1971, oldest operating GFAF (41 years) I've even seen.

    Thanks

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    When you say load side do you mean a non-service panel, ie there is a means of disconnect ahead of this panel?

    Do you have a pic of the neutral buss?

    All answers based on unamended National Electrical codes.

  3. #3
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    Yes, this is a load-side panel ("sub-panel").

    This is the only portion of the "neutral bus" visible at the panel.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  4. #4
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    Micheal is in Chicago, so we know that all equipment grounding is by way of the conduit, eh?

    My guess is that the panel is set up as a suh suh remote panel and no bonding device was ever provided.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  5. #5
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    Quote Originally Posted by John Kogel View Post
    My guess is that the panel is set up as a suh suh remote panel and no bonding device was ever provided.
    Quite possibly - I looked for a bonding jumper/screw and did not find one.

    Still I would like to know for certain where it was supposed to be installed on service equipment.

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  6. #6
    Join Date
    Mar 2007
    Location
    Chicago
    Posts
    164

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    Quote Originally Posted by Michael Thomas View Post
    Quite possibly - I looked for a bonding jumper/screw and did not find one.

    Still I would like to know for certain where it was supposed to be installed on service equipment.
    Hi Mike,

    The bonding jumper screw in the old Pushmatic of this style are generally between lug 3 and 4 (based on your 1st picture). It will not be green and it tends to blend in. It physically looks different in comparison to the lug connections on the bottom of the bus detail and the single screw (next to the bumped-out stops next to the screws) connections on the bus detail above the lugs. I may have a picture of one, if I do, I'll post it.

    Corey


  7. #7
    Stephen G's Avatar
    Stephen G Guest

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    the second photo top breaker allows copper and aluminum...

    Last edited by Stephen G; 04-09-2012 at 02:24 PM.

  8. #8
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    M.T.

    This is not service equipment, its MLO. Should be a lock-nut under the bushing at the bottom left to threaded rigid metal conduit, fitting, wireway, etc.. The ground bar bar when installed/present as load side of service equipment would be mounted upon the back wall to the right most starting at a height below the highest breaker and would extend vertically downward. That back wall section is not visible in your photos.

    You'll see a grounds bus (painted over) installed at D.F.'s site here: http://inspectapedia.com/electric/Pu...ls021-DJFs.jpg

    Last edited by H.G. Watson, Sr.; 04-09-2012 at 06:09 PM.

  9. #9
    Robert Meier's Avatar
    Robert Meier Guest

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    Looks like there is a locknut there.


  10. #10
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    I agree with Robert, I see the locknut.

    All answers based on unamended National Electrical codes.

  11. #11
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    Locknut was (is) there:

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  12. #12
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    Now, I'm wondering what this "yellow button" is...

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  13. #13
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Bonding jumper location on Pushmatic Bulldog panel

    I'm not entirely certain, as it has been many years since I've dealt with a Bulldog Electri Center from Detroit, or an early ITE acquisition panel... I'm also recalling main or lighting main switches that weren't actually breakers used in such, but I'm having a foggy morning.However, if I'm remembering correctly, the same componant parts were used in the manufacture of split buss panels from Detroit. If they had been in a split buss or a main switch not CB panel, I'm thinking that would be where the insulated jumpers would pass so as to connect to the split buss(es), making those "buttons" fillers/insulators/isolators and/or guards, they might be nylon (?).Besides replacements being expensive, costly, older types being unavailable except on the unreliable gray market or used; the breakers themselves are limited in their ability to quickly react to an overload condition (trip type). Panel is of a vintage where direct testing was not undertaken to assure ratings (merely calculated based upon a series of later disproven assumptions). Push button operation and assured fully open or fully closed condition even as indicated, is unreliable, lubrication unreliable, and provides ability for unsafe hack work - provides for direct bolting conductors to buss without use of any special tools, etc. even if unintentional.