Results 1 to 5 of 5
  1. #1
    Join Date
    Mar 2009
    Location
    Charlottesville, Va.
    Posts
    300

    Default Base and Cap Flashing ?

    What is Base and Cap Flashing as referred to in the IRC section R905.2.8.1

    Is Base Flashing the same thing as Drip Edge ?

    Thanks

    R905.2.8.1 Base and cap flashing. Base and cap flashing shall be installed in accordance with manufacturer's installation instructions. Base flashing shall be of either corrosion-resistant metal of minimum nominal 0.019-inch (0.5 mm) thickness or mineral surface roll roofing weighing a minimum of 77 pounds per 100 square feet (4 kg/m2). Cap flashing shall be corrosion-resistant metal of minimum nominal 0.019-inch (0.5 mm) thickness.

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Base and Cap Flashing ?

    Base and cap flashing is flashing and counter flashing.

    base flashing =
    _|

    The base flashing is placed on the roof surface and nailed to it with the upright leg of the flashing held against the wall sheathing.

    cap flashing =
    _|
    |
    The cap flashing has its upper upright leg placed against the wall sheathing and is slid down the wall so that the lower downright leg is over the upright leg of the base flashing, the upper upright leg of the cap flashing is nailed to the wall sheathing while the lower downright leg is not nailed to the base flashing. This allows for movement between the roof and wall and the base flashing and the cap flashing while maintaining a weather-resistant flashing joint.

    _|
    |
    _|

    (hard to draw with lines from the keyboard)

    The base flashing is the base flashing. The cap flashing is the counter flashing.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Mar 2009
    Location
    Charlottesville, Va.
    Posts
    300

    Default Re: Base and Cap Flashing ?

    Oh...I've always referred to the "cap" flashing as counter flashing.


  5. #5
    Stephen G's Avatar
    Stephen G Guest

    Default Re: Base and Cap Flashing ?

    Rob, if you dont learn something each time you come here, you wasted a visit.

    Thanx JP: it clears it up for me too,


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •