Results 1 to 13 of 13
    Feb 2010
    Wenatchee Wa
    Default why double lugged neutrals may not be so good
    We see them all the time but here is an example of why it is not that good of an idea.
    I call this out way too often.
    Don Hester
    NCW Home Inspections, LLC
    cuba_pete's Avatar
    cuba_pete Guest
    Default Re: why double lugged neutrals may not be so good
    Quote Originally Posted by Don Hester View Post
    Pix like these are good to add to "that folder" on my computer.
    Do you happen to know the branch rating for that neutral? What was the rating for the panel? Is that 12 or 14 AWG?
    Feb 2010
    Wenatchee Wa
    It was a 12 ga on a 20 amp.
    Don Hester
    Bert de Haan's Avatar
    Bert de Haan Guest
    Do you mind explaining why that happened Don? I thought the problem with double lugged neutrals was more related to not being able to disconnect the one without the other.
    Feb 2010
    Wenatchee Wa
    Quote Originally Posted by Bert de Haan View Post
    Hard to say exactly but my best guess it that when you double lug you do not have proper torque/connection, then you have a heavy return current on the neutral the resistance causes the neutral to over heat.
    I see the same thing on those darn back stabbed receptacles.
    Just a lack of proper contact.
    I am speculating a bit. But none of the un-grounded conductors had an issue.
    Don Hester
    Lou Romano's Avatar
    Lou Romano Guest
    Why are these neutral conductors tied down on what appears to be a ground bar? Is this in the main panel where they are bonded together or did someone land them in the wrong place? A wider view of the panel would be nice.
    Apr 2009
    NY State
    IMO this is NOT a prime example of why not to "double lug" neutrals. I have seen this just as much, if not more, from individual neutrals.
    While the dreaded "double tapping" neutrals is not code complaint, it is NOT the evil dastardly thing most folks make it out to be.
    The only reason not to double tap is because it is a code violation. Simple as that.
    Lou Romano's Avatar
    Lou Romano Guest
    I agree!
    Feb 2010
    Wenatchee Wa
    Speedy, While I agree this not an evil thing (on the scale of evil ; ). Is it not the reason that is not allowed is the lug here is not designed for multiple grounded conductors and may not have proper contact that will increase resistance. Just saying ; )
    Granted you can do this even without double lugging.
    And like most here we see this all the time without ill effect.
    Don Hester
    Feb 2010
    Wenatchee Wa
    FYI- I really never make a big deal out of this. I tell my clients that though it was never an approved method it was/is very common.
    That can be said about many things in a panel.
    Don Hester
    Robert Meier's Avatar
    Robert Meier Guest
    IMO it should be a big deal. If that neutral is from a MWBC and suddenly 200 volts ends up on the new 65" TV there will really be a problem.
    I think the reason posted by Robert is probably one of the best reasons, outside of the code, to not do this.
    Feb 2010
    Wenatchee Wa
    In this scenario there was no MWBC, that would of been a different beast.
    I do see this quite often with no ill effect. It is not compliant so I make the call.
    Don Hester
