    Saw this today, recommended they have the intake ran outside. It’s in an unfinished basement…ok as is? Looked at the installation manual taped to the side and it shows outside venting for both.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2012
    Location
    Michigan
    Posts
    43

    Default Re: Combustion Air?

    50 cubic feet per 1000 btu is a guideline for combustion. Feed looks to be through cold air return.

    Last edited by Richard Skalski; 05-15-2012 at 06:50 PM. Reason: got a better look a pic.

  3. #3
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Combustion Air?

    Quote Originally Posted by Terry Ewald View Post
    Saw this today, recommended they have the intake ran outside. It’s in an unfinished basement…ok as is? Looked at the installation manual taped to the side and it shows outside venting for both.
    You are correct, it should be installed per the instruction manual. There is no good reason not to.
    That is one of the good features of that furnace, that the intake can be run with the exhaust out to an exterior wall.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  4. #4
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: Combustion Air?

    In my travels I have not seen a requirement for pulling combustion air from the exterior. From the photo I'd say that the installation is correct as an allowable option. Is it as efficient as it could be? No.

    Eric Barker, ACI
    Lake Barrington, IL

  5. #5
    Terry Ewald's Avatar
    Terry Ewald Guest

    Default Re: Combustion Air?

    Thanks


  6. #6
    Join Date
    Jul 2008
    Location
    Chicago
    Posts
    263

    Default Re: Combustion Air?

    Some furnaces require direct venting. Apparently, this Goodman does so you should flag it.

    My Carrier Infinity 96, for example, also does. And as John K. says, there's really no good reason not to do it regardless.


  7. #7
    Join Date
    Mar 2007
    Location
    Knoxville, TN
    Posts
    2,560

    Default Re: Combustion Air?

    Did it show it to the outside as an option or a requirement?


  8. #8
    Terry Ewald's Avatar
    Terry Ewald Guest

    Default Re: Combustion Air?


    I quickly read over it and didn’t see anything mentioning notventing outside…just options for venting in confined spaces.



  9. #9
    Join Date
    Jul 2008
    Location
    Utah
    Posts
    390

    Default Re: Combustion Air?

    There are many "good" reasons to not run the combustion duct to the exterior. Cost and logistics are the primary ones. Since it is a goodman furnace my guess is someone was looking at the low bid.

    One key issue when not running the combustion to the outside is the requirement for a screen or pressure device to simulate the ducting on the intake. The dang things have such a temperamental pressure switch in them that if the set up isn't done exactly how it supposed to be it won't run. My guess is that if it is running, you are good to go.


  10. #10
    Join Date
    Dec 2007
    Location
    Holladay, UT
    Posts
    577

    Default Re: Combustion Air?

    Terry, Is this a confined or unconfined space?

    Tom Rees / A Closer Look Home Inspection / Salt Lake City, Utah
    http://acloserlookslc.com/

  11. #11
    Join Date
    Jan 2012
    Location
    Stamford, CT
    Posts
    38

    Default Re: Combustion Air?

    That Goodman furnace can be installed either as direct vent or non-direct vent. However, if installed as non-direct vent (combustion air does not come from the exterior), Goodman requires that at least one 90 degree elbow be installed on the intake air port (see below and attached). It is missing, so the installation is deficient. Of course, that is not withstanding the calcualtion of confined vs. unconfined space.


    NOTE:
    For non-direct vent installations, a minimum of one 90°
    elbow should be installed on the combustion air intake coupling to

    guard against inadvertent blockage.



    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  12. #12
    Terry Ewald's Avatar
    Terry Ewald Guest

    Default Re: Combustion Air?

    Thanks....I've never seen one with just a 90 on it...but now I know.


  13. #13
    Binford Tools's Avatar
    Binford Tools Guest

    Default Re: Combustion Air?

    No trap in the condensate line? Maybe its run 10 feet to a floor drain vs outside too.