    Default Panel on Floor

    This panel is surface mounted on the wall at floor level.
    I couldn't open the cover because the rug blocks the screws, and I'm aware of accessibility in front BUT - Does a panel have a minum mounting height requirement?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral
    Ken Amelin
    Cape Cod's Best Inspection Services
    www.midcapehomeinspection.com

  2. #2
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: Panel on Floor

    Quote Originally Posted by Ken Amelin View Post
    Does a panel have a minimum mounting height requirement?
    No it doesn't.

    Eric Barker, ACI
    Lake Barrington, IL

  3. #3
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Panel on Floor

    We've had this height discussion before. I thought it had been determined there was no minimum height but there was a max height. Also I vaguely remember a discussion about working around the minimum height by citing sufficient accessibility ... I'm sure someone with a better brain will have the answers ... Jerry?
    Did you check the addition structure, etc.? My guess is the panel used to be fine until they built the addition and didn't move it.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  4. #4

    Default Re: Panel on Floor

    Wow, that would scare me... especially since it looks like it's in a kid's room? How could it be safe?

    Welmoed Sisson
    Inspections by Bob, LLC, Boyds, MD
    "Given sufficient thrust, pigs fly just fine."

  5. #5
    Robert Meier's Avatar
    Robert Meier Guest

    Default Re: Panel on Floor

    There is no minimum height requirement providing that one can remove the cover and access the panelboard. You might argue that it's within the vicinity of easily ignitable material if the carpet is easily ignitable.


    240.24 Location in or on Premises.
    (D) Not in Vicinity of Easily Ignitible Material. Overcurrent
    devices shall not be located in the vicinity of easily
    ignitible material, such as in clothes closets.



  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Panel on Floor

    Quote Originally Posted by Robert Meier View Post
    There is no minimum height requirement providing that one can remove the cover and access the panelboard. You might argue that it's within the vicinity of easily ignitable material if the carpet is easily ignitable.
    "providing that one can remove the cover and access the panelboard"

    That is the minimum height.

    I also like the argument about easily ignitable material, especially as we all know that some of carpet could get caught between the cover and the enclosure and be in the panel. Of course, though, that argument would go away when the panel is raised enough so the cover can be removed and the panel made fully accessible.