Thread: service neutral
05-29-2012, 09:33 PM #1
service neutral
Is this one a concern? IS it possible a failed service breaker?
05-30-2012, 03:03 AM #2
Re: service neutral
Kind of looks like anti-oxidant paste on the strands. If there was an overheating condition, you'd see scorching on the sheathing. It does look a bit stained and darker but not enough to tell if overheating took place.
05-30-2012, 10:06 AM #3
Re: service neutral
Why would you think showing the neutral would point to a failed breaker?
If the main breaker had failed there would be no power.
05-30-2012, 10:44 AM #4
Re: service neutral
Here's a scorched connection for comparison. 1974 Al wiring. This white wire is still doing its job, but needs repair. And it should have been marked red or black.
As a matter of fact, this wire has been spliced once already. A 15 amp 240 volt breaker is supplying a 40 gallon water heater through a compromised Al feeder. I hope the electrician will do the right thing here for my clients.
05-30-2012, 01:08 PM #5
Re: service neutral
Thanks.
I mean failed to trip once overload.
05-30-2012, 02:26 PM #6
05-30-2012, 04:23 PM #7
05-30-2012, 05:02 PM #8
Re: service neutral
You could have a terminal overheat well under its ampacity and not trip a breaker. All you need is a poor connection.
A neutral on an improperly wired multiwire branch circuit could be carrying 2x the current of the hots. This will not trip a breaker either.
05-31-2012, 06:13 PM #9