Results 1 to 6 of 6
  1. #1
    Join Date
    Apr 2010
    Location
    Connecticut
    Posts
    49

    Default Hip Rafter Attachment And Brace

    This hip rafter does not appear to be properly attached.
    Can any of you framing experts suggest a better method?
    The support brace is poorly supported below and will need to be removed.

    HIP RAFTER.JPG

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: Hip Rafter Attachment And Brace

    From what I see in the photo the hip rafters appear to be braced against the ridge, which is a proper practice. If they terminated below the ridge they would need vertical support. The vertical support in the photo appears to be a temporary brace used during construction.


  3. #3
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Hip Rafter Attachment And Brace

    That's kind of a tricky question.
    The rafter you are indicating is a Lam beam as opposed to a regular wood beam. Installing a lam beam would tend to indicate that there is a load factor that needs to be met per the approved drawings. Did someone put that in for a reason or because it was supposed to go somewhere else (say the adjacent hip) and they used it because they had it.
    The adjacent hip appears to be oversized to fully support the rafters but is too small to fully support the lam beam. Definition in the pic isn't good enough to see if there are proper nails in place.
    If its nailed properly and there isn't a specific load need for this to be a lam beam then it will probably ok.
    The installed stud could be fine if supported on a bearing wall or sufficient joist. If sitting on a small 2x8 ceiling joist in mid span you could end up with drywall cracking.
    This is one of those iffy scenarios thats hard to decipher unless onsite. Is the rafter going to drop or the roof going to collapse? Probably not. Could they end up with some cracking? Possible.
    I wouldn't sign off on it as is. Require someone to provide the approved Plans or refer it.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  4. #4
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Hip Rafter Attachment And Brace

    You have a pic from further back, or another angle of the hip rafter?

    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

  5. #5
    Join Date
    Apr 2010
    Location
    Connecticut
    Posts
    49

    Default Re: Hip Rafter Attachment And Brace

    Quote Originally Posted by ROBERT YOUNG View Post
    You have a pic from further back, or another angle of the hip rafter?
    Sorry this is the only view. This is a new construction house and I'm now in contact with the builder. My clients will get taken care of.


  6. #6
    Join Date
    Jul 2010
    Location
    Summerville, South Carolina
    Posts
    116

    Default Re: Hip Rafter Attachment And Brace

    Quote Originally Posted by William Kievit View Post
    This hip rafter does not appear to be properly attached.
    Can any of you framing experts suggest a better method?
    The support brace is poorly supported below and will need to be removed.

    HIP RAFTER.JPG
    There's really not enough information from the photo to tell if that brace or another better constructed brace is needed. I would tend to put a brace at the junction of the hip cripple and the valley. The Lam beam does suggest a longer rafter with more load but not necessarily. It may have just been used to catch the plywood better. If you want to know more about roof framing check out my book The Roof Framers Field Manual ...... Yes....this is a shameless self promotion....


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •