    Default Flashing needed??

    On both sides of my chimney, there appears to be water damage to my siding where the chimney meets the roof. The damage also goes down the back side of the chimney on both the right and left corners as the paint is bubbling. Would flashing correct this problem? Any help is appreciated. Pictures are below. I did have my roof replaced, complete tear off, 2 years ago when I bought my house. Thanks!

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Flashing needed??

    Quote Originally Posted by Jennifer Walterlin View Post
    On both sides of my chimney, there appears to be water damage to my siding where the chimney meets the roof. The damage also goes down the back side of the chimney on both the right and left corners as the paint is bubbling. Would flashing correct this problem? Any help is appreciated. Pictures are below. I did have my roof replaced, complete tear off, 2 years ago when I bought my house. Thanks!
    .
    Jennifer,

    Looks like there is metal flashing installed behind the siding.

    A 1 1/2 inch gap between the siding and the rooftop is recommend to mitigated water wick-in up the siding causing the shown rot.

    The damage has already been done.
    .

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  3. #3
    Garry Blankenship's Avatar
    Garry Blankenship Guest

    Default Re: Flashing needed??

    I need help here, but if there is flashing in play, I believe it should be under the siding and on top of the roofing. So I'm inclined to believe there is none. Also what Billy says. The siding is too close to the roof surface. I suspect your roofer was inexperienced or in too much of a hurry.


  4. #4
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Flashing needed??

    Quote Originally Posted by Garry Blankenship View Post
    I need help here, but if there is flashing in play, I believe it should be under the siding and on top of the roofing. So I'm inclined to believe there is none. Also what Billy says. The siding is too close to the roof surface. I suspect your roofer was inexperienced or in too much of a hurry.


    You're confusing "flashing" and "counter-flashing" again, Garry B.

    To the OP, search the subject here. Michael Thomas and others have posted many diagrams, links, etc. and there have been myriad discussions on the subject of pitched roofing surfaces intersecting vertical planes and projections.

    There doesn't appear to be any canting, cricket, or kick-outs either.

    Find your roofing contract and check the scope of work.


  5. #5
    Join Date
    Oct 2010
    Location
    Tolland, CT
    Posts
    33

    Default Re: Flashing needed??

    the wood should be off the roof. 1 to 1-1/2"
    step flashing shouldbe visable as it goes under the siding or counter flashing. roof shingles cover the step flashing on the layer below.
    so it is shingle step flashing shingle step flashing etc along the sides.

    Mike


    Quote Originally Posted by Jennifer Walterlin View Post
    On both sides of my chimney, there appears to be water damage to my siding where the chimney meets the roof. The damage also goes down the back side of the chimney on both the right and left corners as the paint is bubbling. Would flashing correct this problem? Any help is appreciated. Pictures are below. I did have my roof replaced, complete tear off, 2 years ago when I bought my house. Thanks!



  6. #6
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Flashing needed??

    I am also not seeing a diverter or "kick-out" flashing to direct water into the gutter. Hmmm... let's see if I can find a diagram...

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  7. #7
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Flashing needed??

    I see the step flashing is in there in pic 1 and 3. The new shingles are thicker and this is a common result - wood trim touching the roof. Roofers don't normally do carpentry alterations. A carpenter needs to carefully trim the wood without cutting the flashing. Then add the kickouts from Gunnar's post.

    Soft spots in the siding can be cleaned up and filled with an epoxy filler, then repainted.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Flashing needed??

    Like Billy said, it needs at least 2" between the bottom of the siding and trim and the top of the shingles.

    And as Gunnar said, it needs a kickout flashing at the bottom where the overhang meets the side of the chimney.

    Depending on how wide the chimney is, it may need a cricket on the high side of the chimney.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: Flashing needed??

    Quote Originally Posted by H.G. Watson, Sr. View Post
    There doesn't appear to be any canting, cricket, or kick-outs either.
    Sorry HG, I didn't notice that you already mentioned that. For some reason, I saw the cricket...

    I guess I need to slow down a little.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  10. #10
    Jennifer Walterlin's Avatar
    Jennifer Walterlin Guest

    Default Re: Flashing needed??

    I remember there being a cricket on the roofing quote, but I haven't been on the roof to look at anything since I just assumed the roofer did it right. I'll get a hold of the company that did it and have them come back out to look at it. I'll mention the cricket, cutting back the siding and the kickback flashing to him and see what he says. Those are pretty standard procedures when doing a complete tear off and new shingles, right?! Well, except cutting back the siding... wouldn't expect the roofing company to do that but he could have at least mentioned it to me 2 years ago. But thanks so much for everyone's help!! This single homeowner appreciates it VERY much!


  11. #11
    Join Date
    Jan 2011
    Location
    Parkersburg, WV
    Posts
    9

    Default Re: Flashing needed??

    Jennifer,

    The posted info is good.
    Check chimney cap for leakage and slope. Most are inadequate. Replace with welded seam stainless if needed.
    Since this is a reroof, proper procedure would be to inspect existing flashing, particularly step flashing, for corosion, breaks, etc. Probably replace and have counterflashing installed. Replace rotted wood with Azek or similar- probably replace all wood and install moisture barrier integrated with new chimney cap and step flashing.
    Kickouts should be welded, soldered or one-piece plastic like Dryflekt or Raintek. I did a survey in Chicato several years ago and found at least 30% of field-formed (cut, bent and caulked) kickouts leaked. Above diagram is good, but not perfect.
    If cricket is not installed properly, have the whole mess removed and rebuilt. Easier and better than a hodgepodge of repairs and patches. Keeping the sheathing 2" or more above the shingles is common sense and probably required by code. Makes it easier to replace the shingles in the future, especially if counter-flashing is removeable.
    Also, keep ends of gutters at least 1/2 inch away from chimney for expansion.
    Call me if I can help.
    Mike Minigh
    MoistureTech
    304-904-6055


  12. #12
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Flashing needed??

    Appears to be caulking used to replace the rotted wood or an attempt to seal damage.

    The wood has been deteriorating for sometime, likely prior to new roof.