    Default Zinsco panel. Split bar?

    Is this a split bus bar. Feeders come in from meter, no disconnect. Disregard the tank.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Zinsco panel. Split bar?

    I've never seen one of those before ...

    That's not a split bus panel in the normal sense in that the 'mains' part of the panel is limited to 6 breakers and one of those 'mains' feeds the other bus section - that one is more of a 'double bus' panel ... weird, never saw one before.

    Was the cover factory looking? If not, may have been someone's idea of taking an oversize enclosure and putting to panelboard interiors in it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Zinsco panel. Split bar?

    From what I can see the left bar is the mains and one of those feeds the right side. New to me but looks like it is just a slightly different layout from the traditional split buss panel.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  4. #4
    Garry Blankenship's Avatar
    Garry Blankenship Guest

    Default Re: Zinsco panel. Split bar?

    Copy the never seen one of those before. Zinco's version of the "double wide". Based on the wires and C/Bs I can see; the entire right side is a, ( split ), bus. Looks to be fed by a C/B in the "main" section. There are already the maximum six allowed disconnects in the left side, but plenty of room for more ( ? ). As best I can determine, it's code compliant for the vintage, ( until another C/B is added to that left / main disconnect side ). Very unique !


  5. #5
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: Zinsco panel. Split bar?

    Never have seen that in a 1Ø panel but the double row was common in Zinsco 3Ø panels for plug-in breakers, which are a weird beast all by themselves. 3Ø bolt-on Zinsco panelboards are "normal" in the way they are configured.

    Edit: If you look closely at the picture, there are a set smaller lugs adjacent to the main lugs, I suspect there was a factory jumper installed to the right side section. It may even be old enough to have copper bus.


  6. #6
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Zinsco panel. Split bar?

    I thought is was just me, I told the buyer I had never seen one like this before.


  7. #7
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Zinsco panel. Split bar?

    Here is the cover

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  8. #8
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Zinsco panel. Split bar?

    There is a 70amp breaker on the left side which feeds the right bar. The left bar is fed by the feeders coming in from the meter, there is no service. So you cant shut off the power with six or fewer. I am uning the usual reporting for zinso but would you identify the split bus as a hazard.


  9. #9
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Zinsco panel. Split bar?

    Double trouble!

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  10. #10
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: Zinsco panel. Split bar?

    I too, have never seen anything like that. But as inspectors, we get an easy out reporting it. Just write something like Zinsco panels have documented problems. Current industry recommendation is to replace the panel. Have a licensed electrician evaluate and/or replace the panel as necessary.

    But for our edification as inspectors, knowing more about a beast like that is certainly worthwhile.


  11. #11
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Zinsco panel. Split bar?

    The restrictions on the labeled equipment likely prohibit use of the half-size 2-pole minis on the externally supplied Mains side when employed as service equipment (i.e. full-size only often by cat. number or type breakers). Apparently of a non-CTL vintage.

    Non MCB, or six or fewer, is not an issue of issue since a its main power feeder-supplied and not a "service" supplied panel (as you said). Six are present (the five 2-P 120/240 need to be tied plus the lighting main).

    Not unusual to have a back fed breaker feeding a "lighting mains" on a split bus. Its not the first vintage panel pictured on the forum to use conductors to the sub-buss on a split bus panel, nor the first zinsco.

    Check the fine print on the labeling - the "stab rating" (max) for the "main" side likely limited (usually at the vintage to 60 A). There is also likely "max" as in cumulative total ratings (not load calculations) for the breakers attached to each set of busses.

    Side-by-side split buss (often installed side-ways in vintage installations even with OFF "up" on half) also not unusual.

    Sadly, the remodel of the area nixed any "grandfather" status - as the installation of the new cabinets which now encroach on the equipment space. Rip out the cabinets or move the location for the replacement panel. Installing cabinets in a new location might not have required permit - but violating the electrical code then and at the time of the newer cabinet's installation in a new, not previously occupied by cabinetry, location (note cabinet door swing direction) violated the electricl code at the time of (the cabinet's) installation. Hopefully the washer or electric dryer hookups aren't also immediately below the new wall cabinet (further encroaching - when installed - the equipment access zone) in what I'm guessing is the newly 'updated' laundry area.

    Last edited by H.G. Watson, Sr.; 06-29-2012 at 11:25 PM.

  12. #12
    Keith Gipe's Avatar
    Keith Gipe Guest

    Default Re: Zinsco panel. Split bar?

    Yeah, crazy looking. Not seen one before. Doesn't appear to qualify as a split-bus since the installation looks like it would allow more than six double pole breakers on the "main" side. If so, it should have been installed with a main disconnecting means. This looks like an expandable panelboard which allows the installer to put in a single panelboard or expand it to accept two. All split-bus panels I have seen are arranged with the six mains on top. One of the six feeds the bottom bus with the lower capacity breakers on the bottom.


  13. #13
    Join Date
    Mar 2007
    Location
    Nampa, Idaho
    Posts
    601

    Default Re: Zinsco panel. Split bar?

    Here is my canned comment for Zinsco Panels or Sylvania's with Zinsco breakers.

    This property has a Zinsco brand main service panel and circuit breakers. These panels and circuit breakers are known to have a variety of problems including:

    *Buss bars possibly made from aluminum alloy and are more likely to oxidize and corrode
    *Breakers that don't trip under normal overload conditions
    *Breakers that appear to be tripped when they're not

    You should be aware that these panels do not offer the level of overcurrent and fire protection provided by most other electrical panels and circuit breakers. Becasue of this we recommend that the panel be updated and replaced.