Results 1 to 3 of 3
  1. #1
    Join Date
    Mar 2012
    Location
    Cleveland, Ohio
    Posts
    52

    Default Question regarding proper gas line shutoffs

    A 1971 multi family aparment unit had numerous gas shutoffs installed of this type. I could not find any "WOG" markings on the fittings. is there any other way to distinguish that these (blue handle) shutoffs are not water line shutoffs? If so, how would one tell with certainty?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Question regarding proper gas line shutoffs

    I could be wrong here but I've never known gate valves to be approved for gas. (the blue handle one)
    The other issue is the old boiler gas valve. (the silver one in Pic 2)
    A- those are known leakers
    B- that one looks like it might have a plugged pilot tube tap, if so definitely get that thing out of there.
    Recommend client get rid of both and install one new approved gas cock.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  3. #3
    Join Date
    Jul 2009
    Location
    Lanham, MD
    Posts
    86

    Default Re: Question regarding proper gas line shutoffs

    The valve with the blue handle is a compression stop valve (it's not a gate valve) and definitely not allowed for gas service. The packing is prone to leaking around the packing nut and the internal washer is likely not compatible with natural gas.
    As mentioned, both valves should be replaced with a proper gas cock.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •