07-28-2012, 02:40 AM #1
Can You use a smaller coil to a bigger condenser
Do these two work together
Whirlpool M# WEMIP50Cw-1
S# 6209D05207
Nordyn
M#NS4BD-O60KA
S# NSA090400o71
07-28-2012, 05:51 AM #2
Re: Can You use a smaller coil to a bigger condenser
It depends on several factors.
You can get some hvac technical info here:
HVAC-Talk: Heating, Air & Refrigeration Discussion - Powered by vBulletin
www.BAKingHomeInspections.com
07-29-2012, 03:25 PM #3
umm, bad idea. Symptoms, poor performance, compressor failure due to high superheat.
07-30-2012, 08:47 AM #4
I concur with the statements above. I'd also add that you could see frosting and freezing of the coil more often as well.
It is generally a bad idea to under-size your coil.
07-30-2012, 01:44 PM #5
08-20-2012, 12:33 PM #6
Blower motor to small
What would happen if You put a smaller blower motor. On a 5 ton system say a 1/2 or a 1/4 horse power motor. The system still doesn't work they replaced the coil with a 5 ton coil.
09-02-2012, 01:40 PM #7
09-03-2012, 07:28 PM #8
I've run into this a few times lately and have called for HVAC to check it. Surely there must be some reason that the sizing is supposed to be matched, not larger or smaller. Mismatching must be a problem, otherwise why label the evaporator? The unit doesn't say "OK for 4 ton or smaller compressor".
END GLOBAL WHINING