    Default New metal flue liner

    A new flex metal flue liner and cap has been installed in this solid fuel burning fireplace. I doesn't look right to me but not very confident of my flue pipe knowledge. Any help here is greatly appreciated. Picture 3 is the photo of the flue looking up from inside the fireplace.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: New metal flue liner

    That lower end of the liner is unacceptable in my eyes. The fireplace is unsafe to use, therefore, a useless hole in the house.

    Speaking of the roof, what have they done up there? The whole mess is the work of an amateur. The roof will probably leak at the chimney flashing and ridge, and the shingles are susceptible to wind damage.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  3. #3
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: New metal flue liner

    Undersized badly. This liner is probably at best one fourth of the size required for a see-through fireplace.

    Liner transition to smoke chamber improper. For one, they used regular fiberglass insulation instead of ceramic fiber or listed cementitious cast insulation. Should be parged over with furnace cement.

    Is this a single sided fireplace where they blew out the back wall and made it a ST or ST from the ground up? The original flue tile looks way undersized from the get-go.

    This looks similar to the work of the scammers. They come in for almost do initial charge, sweep, then tell the homeowner they MUST reline at once! They bully the homeowner into relining and they just happen to be carrying the liner with them and can do it on the spot. Let me tell you, NO professionals I know of carry liners around with them because you have to size them by diameter and length, different hardware such as terminations to choose from, etc.

    More than enough grounds to call for a Level II inspection.

    Keep the fire in the fireplace.

  4. #4
    Join Date
    Jul 2009
    Location
    Spokane, WA
    Posts
    116

    Default Re: New metal flue liner

    The home is a bank repo so not a whole lot of info. The liner and cap looks brand new. It looks like flex duct like you would see on a clothes dryer only bigger around. If installed correctly is it acceptable for this material to line a solid fuel chimney? Maybe the previous occupants were in the middle of converting the fireplace to a gas log set? I'm going to return to the home today to pick up the Radon test. I will take a few more photos. If nothing else you will get a better idea of whats going on with the roof. Thanks for your input.


  5. #5
    Join Date
    May 2012
    Location
    Western Maryland
    Posts
    131

    Default Re: New metal flue liner

    Geez...looks like they duct taped the lower edge. You know, the part right above the flame. Must be fireproof tape

    Mark Fisher
    Allegany Inspection Service - Cumberland MD 21502 - 301-722-2224
    Home Inspections, Mold Testing, Thermal Imaging

  6. #6
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Talking Re: New metal flue liner

    Some liner mfrs use tape to protect the rough cut edges for shipping and handling. Pros know to remove the tape before installation. Some use different color tapes for different thicknesses of metal while others use color coding for various alloys.

    I can't tell if its stainless steel or aluminum from here much less what alloy, which is why you need a level II.

    It doesn't matter if they were going to install gas logs or not, you still size the liner to the fireplace suitable for solid fuel application. The code assumes the fireplace could be converted back to woodburning at any time. Many amateurs will refer to the gas sizing tables, which is wrong. Those are for listed gas appliances, which an open hearth fireplace is not.

    All together now class, let's say: "Level II"

    Keep the fire in the fireplace.

  7. #7
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: New metal flue liner

    Quote Originally Posted by Bob Harper View Post
    .

    All together now class, let's say: "Level II"
    .
    Bob your The Original Sham WoW Infomercial - YouTube is showing.
    .
    But I prefer Vince with Slap Chop (Long version) - YouTube .
    .

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  8. #8
    Join Date
    Jun 2010
    Location
    San Luis Obispo
    Posts
    26

    Default Re: New metal flue liner

    What Bob Said, undersized, bad install etc.

    Also double sided fireplaces are famous for spilling smoke, even if not with undersized flue that has been lined with undersized liner.

    We get a lot of customers who think that installing a gas log set is the fix for this. However once lit the gas log set (without ODS) will burn forever spilling now "invisible" fumes (at least a wood fire will burn down and out at some point).