Results 1 to 3 of 3
  1. #1
    Join Date
    Mar 2007
    Location
    Ingleside Illinois
    Posts
    118

    Smile Water pipe next to panel

    Neighbor sold her home and was told she had to move a water pipe. She has a copper water pipe running vertical 5 inches to the side of her panel. Its doesn't run over the top of the panel, I don't understand the issue. Am I missing something ?

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Water pipe next to panel

    Unless it impinges on the 30" width requirement for the panel workspace it is not an NEC issue.

    All answers based on unamended National Electrical codes.

  3. #3
    Join Date
    Mar 2007
    Location
    Ingleside Illinois
    Posts
    118

    Default Re: Water pipe next to panel

    The panel has 30 inches on both sides so I didn't it was an issue.

    Last edited by Bill Wieczorek; 08-20-2012 at 01:00 PM.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •