    Default Condenser amperage draw

    Many years ago I was taught to check each leg of the condenser circuit for amperage draw and compare with the RLA rating on the unit (easy to do when I have the panel open anyway). I had a question about a result from yesterday, but in perusing this section of the forum, it doesn't seem to be a common approach; the common focus seems to be temp drop.

    This is not my primary area of expertise (obviously) and, believe it or not, most houses I see do not have central A/C, but I've used a 65%-75% of RLA as a baseline, significantly higher or lower indicating potential issues (usually low refrigerant charge or failing motor).

    Please enlighten me!

    Similar Threads:
    Crawl Space Creeper
    Mark Fisher
    Allegany Inspection Service - Cumberland MD 21502 - 301-722-2224
    Home Inspections, Mold Testing, Thermal Imaging

  2. #2
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Condenser amperage draw

    Quote Originally Posted by Mark Fisher View Post
    Many years ago I was taught to check each leg of the condenser circuit for amperage draw and compare with the RLA rating on the unit (easy to do when I have the panel open anyway). I had a question about a result from yesterday, but in perusing this section of the forum, it doesn't seem to be a common approach; the common focus seems to be temp drop.

    This is not my primary area of expertise (obviously) and, believe it or not, most houses I see do not have central A/C, but I've used a 65%-75% of RLA as a baseline, significantly higher or lower indicating potential issues (usually low refrigerant charge or failing motor).

    Please enlighten me!
    Amperage and temperature differential are both indicators of the condition of the system. The 65-75% is a good average but you have to add in the fan RLA. Just like the temperature differential you have to take into account other factors that can effect the readings. Ambient air temps, humidity levels, length of time the system has been running, and air flow. The things we as home inspectors can see or measure are only estimates of the condition and should be used to determine whether we recommend further evaluation or not. One of the things many inspectors do not use as a tell is the direction of airflow at the outdoor/condenser unit. If the air flow is horizontal there is a good chance the coils are blocked by dirt or bent fins, it can also indicate missing cowling or too small of fan blades. A piece of surveyors tape on your inspection probe shows the direction of airflow with an easy swipe over the top of the unit.

    The beatings will continue until morale has improved. mgt.

  3. #3
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Condenser amperage draw

    Quote Originally Posted by Robert Meier View Post
    Why would the unit only be operating at 65-75% of the RLA?
    RLA is rated load amps or 100% of what the motor can handle. You wouldn't run your car at red line all the time would you?

    The beatings will continue until morale has improved. mgt.

  4. #4
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Condenser amperage draw

    Quote Originally Posted by Robert Meier View Post
    RLA is the actual running current of the compressor when normally loaded. It should be operating at or near it's 100% rating. The MCA is used to determine the conductor size and has a factor of 25% added by the manufacturer of the equipment. The two terms are not interchangeable.
    With your logic and interpretation the current should be 125% or more on hot humid days. I, and I'm sure Mark Fisher, can tell you the measured current of a properly running system is normally in the 65-75% range.

    The beatings will continue until morale has improved. mgt.

  5. #5
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Condenser amperage draw

    Measured at the breaker I would expect to find 14-15 amps on that unit.

    The beatings will continue until morale has improved. mgt.

  6. #6
    Join Date
    May 2012
    Location
    Western Maryland
    Posts
    131

    Default Re: Condenser amperage draw

    Quote Originally Posted by Robert Meier View Post
    I'm just wondering if we're talking about the same thing, meaning the RLA. Here's a photo from an AC unit. The RLA of the compressor is 19.9 amps. Are you saying under normal conditions this will only draw 65-75% of it's rating?

    Most of the time, yes, that is a typical reading for a system cooling nicely. Much lower usually means a low refrigerant charge. Much higher I think of as the compressor motor 'straining' (bearing going or some such - like I said, not my area of expertise). Rarely see anything at or over the plate RLA value and those have been bad compressor motors.

    That's been my experience.

    Mark Fisher
    Allegany Inspection Service - Cumberland MD 21502 - 301-722-2224
    Home Inspections, Mold Testing, Thermal Imaging

  7. #7
    Join Date
    May 2012
    Location
    Western Maryland
    Posts
    131

    Default Re: Condenser amperage draw

    Vern, my original reason for posting was this: I typically have only a tenth or two amperage difference between legs. Monday was .5 Amps.

    What does that tell you and how big a difference is an issue?

    Mark Fisher
    Allegany Inspection Service - Cumberland MD 21502 - 301-722-2224
    Home Inspections, Mold Testing, Thermal Imaging

  8. #8
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Condenser amperage draw

    Quote Originally Posted by Mark Fisher View Post
    Vern, my original reason for posting was this: I typically have only a tenth or two amperage difference between legs. Monday was .5 Amps.

    What does that tell you and how big a difference is an issue?
    The difference between legs is a result of 120v loads in the unit or leakage. If the unit doesn't have a neutral then there is a current leak somewhere.

    The beatings will continue until morale has improved. mgt.

  9. #9
    Join Date
    May 2012
    Location
    Western Maryland
    Posts
    131

    Default Re: Condenser amperage draw

    Current leak?

    Mark Fisher
    Allegany Inspection Service - Cumberland MD 21502 - 301-722-2224
    Home Inspections, Mold Testing, Thermal Imaging

  10. #10
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Condenser amperage draw

    Quote Originally Posted by Mark Fisher View Post
    Current leak?
    Most likely leak source would be the compressor windings. Worst enemy to the compressor is moisture which converts into acid when mixed with the refrigerant. The acid deteriorates the varnish like insulation of the winding wires and with the refrigerant cooling the windings by flowing over them there is a resistive path for current flow to the case of the compressor.

    The beatings will continue until morale has improved. mgt.

  11. #11
    Join Date
    May 2012
    Location
    Western Maryland
    Posts
    131

    Default Re: Condenser amperage draw

    Interesting. So how big a difference between the legs indicates an issue?

    Mark Fisher
    Allegany Inspection Service - Cumberland MD 21502 - 301-722-2224
    Home Inspections, Mold Testing, Thermal Imaging

  12. #12
    Join Date
    Mar 2008
    Location
    Charlotte NC
    Posts
    2,304

    Default Re: Condenser amperage draw

    Quote Originally Posted by Mark Fisher View Post
    Interesting. So how big a difference between the legs indicates an issue?
    I don't have a number that I can give. I'm sure the manufacturer would say any current leak must be fixed, meaning replace the unit. The practical answer would take into account the size and age of the compressor, will it last out its normal lifespan before going all the way to the bad? Judgment call, in my opinion .5amp is starting to look a little dodgy.

    The beatings will continue until morale has improved. mgt.

  13. #13
    Join Date
    May 2012
    Location
    Western Maryland
    Posts
    131

    Default Re: Condenser amperage draw

    Thanks, Vern. Great info!

    Guys, this simple test can tell you a lot about the compressor motor. We already have the breaker panel open, so why not? Temp drop tells us about the overall system, but the compressor motor is the high-dollar item in the mix.

    Mark Fisher
    Allegany Inspection Service - Cumberland MD 21502 - 301-722-2224