    Question 50 amp 3 pole 4 wire service?

    Needing to wire service for an RV. Uses a "50 amp 120/240-volt 3pole 4 wire grounding service" hook up. Wiring to a 70 amp breaker box directly below a meter base on a temp pole set up. Will be running wire about 40 ft. underground to four pole plug in a metal box, which is where cord for trailer will plug into. Breaker box has a common ground/neutral buss bar, not seperate ones. My question is, Seeing as the ground and neutral are common in the breaker box, could I run just an encased 4/3 cable to the plug box and then jumper the ground and neutral wires at the plug intead of getting another wire to run along side the encased wires? They will be coming off the same buss in the breaker box anyway, why get the extra wire? Or do I need to get another breaker box, with a seperate ground and neutral buss ( which will more than likely be bonded in the breaker box )?

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: 50 amp 3 pole 4 wire service?

    No offense Tony but if you have to ask those questions, you really should hire an electrician. RV service looks simple but can be deadly.
    But no, you cannot omit the 4th wire. There is a separate ground / neutral for a reason.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  3. #3
    Tony Stanek's Avatar
    Tony Stanek Guest

    Default Re: 50 amp 3 pole 4 wire service?

    So Jim, I need to get another breaker/service panel with a seperate grounding bus????


  4. #4
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: 50 amp 3 pole 4 wire service?

    Quote Originally Posted by Tony Stanek View Post
    So Jim, I need to get another breaker/service panel with a seperate grounding bus????
    Tony
    Jim said what you need to do.
    Quote Originally Posted by Jim Luttrall View Post
    No...you.. should hire an electrician.
    RV service...can be deadly.


    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  5. #5
    Join Date
    Feb 2008
    Location
    New York
    Posts
    869

    Default Re: 50 amp 3 pole 4 wire service?

    Maybe I'm not understanding your description, but I question your whole installation. For 120 you need a neutral, and for 240 you need 2 hots; is the 3rd wire your neutral? So where is your ground? And an additional isolated ground (or grounding rod)is most likely required.

    Even if you supply the labor to dig the trench, it sure makes sense to have a real electrician oversee the install and make the connections.

    Steven Turetsky, UID #16000002314
    homeinspectionsnewyork.com
    eifsinspectionsnewyork.com

  6. #6
    Join Date
    Mar 2012
    Location
    Northern Indiana
    Posts
    98

    Default Re: 50 amp 3 pole 4 wire service?

    A branch circuit does not require a ground rod or grounding electrode system.


  7. #7
    Join Date
    Mar 2012
    Location
    North Central Texas
    Posts
    491

    Default Re: 50 amp 3 pole 4 wire service?

    As long as you have a grounding conductor present and properly connected in the cable going to the RV no ground rod is required. If a generator is included in the mix it may be required. See: http://www.osha.gov/OshDoc/data_Hurr..._generator.pdf

    Texas Inspector
    http://www.texasinspector.com
    What the plainspoken man lacks in subtlety, he makes up in clarity.

  8. #8
    Join Date
    Feb 2008
    Location
    New York
    Posts
    869

    Default Re: 50 amp 3 pole 4 wire service?

    Quote Originally Posted by Brad Richter View Post
    A branch circuit does not require a ground rod or grounding electrode system.
    Does the 70 Amp breaker being fed on the pole need a grounding electrode? As far as the metal box housing the 4 prong outlet being fed from 40' away underground, I always thought when running a feeder underground to a remote location, like a garage or satellite dish, Etc. you need a grounding system.

    Does he not need the 4th conductor? He is talking about using a neutral as a ground to eliminate a 4th conductor.

    Last edited by Steven Turetsky; 09-26-2012 at 06:09 AM.
    Steven Turetsky, UID #16000002314
    homeinspectionsnewyork.com
    eifsinspectionsnewyork.com

  9. #9
    Al Neuman's Avatar
    Al Neuman Guest

    Default Re: 50 amp 3 pole 4 wire service?

    You can't use a 70 Amp breaker with a 50 Amp receptacle in the first place......

    Like the others, I recommend you hire a competent electrician.


  10. #10
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: 50 amp 3 pole 4 wire service?

    Quote Originally Posted by Steven Turetsky View Post
    So where is your ground? And an additional isolated ground (or grounding rod)is most likely required.
    You need to read up on the purpose and function of grounding electrodes and equipment grounds.

    A grounding electrode (ground rod) can NEVER take the place of an equipment ground. The earth is NEVER to be used as a path for fault current. EVER.


  11. #11
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: 50 amp 3 pole 4 wire service?

    Quote Originally Posted by Tony Stanek View Post
    Needing to wire service for an RV. Uses a "50 amp 120/240-volt 3pole 4 wire grounding service" hook up. Wiring to a 70 amp breaker box directly below a meter base on a temp pole set up. Will be running wire about 40 ft. underground to four pole plug in a metal box, which is where cord for trailer will plug into. Breaker box has a common ground/neutral buss bar, not seperate ones. My question is, Seeing as the ground and neutral are common in the breaker box, could I run just an encased 4/3 cable to the plug box and then jumper the ground and neutral wires at the plug intead of getting another wire to run along side the encased wires? They will be coming off the same buss in the breaker box anyway, why get the extra wire? Or do I need to get another breaker box, with a seperate ground and neutral buss ( which will more than likely be bonded in the breaker box )?
    Sorry Tony, there is SO much wrong here, in practice and in theory, that I agree with the others. PLEASE hire an electrician to do this job correctly.
    Just knowing how to connect wires does not mean one is capable of doing a job like this safely. v


  12. #12
    Join Date
    Feb 2008
    Location
    New York
    Posts
    869

    Default Re: 50 amp 3 pole 4 wire service?

    Quote Originally Posted by Speedy Petey View Post
    You need to read up on the purpose and function of grounding electrodes and equipment grounds.

    A grounding electrode (ground rod) can NEVER take the place of an equipment ground. The earth is NEVER to be used as a path for fault current. EVER.
    I never said that an equipment ground takes the place of a grounding electrode. I mentioned a few things that may be necessary, and also stated that His description wasn't too clear (to me).

    Steven Turetsky, UID #16000002314
    homeinspectionsnewyork.com
    eifsinspectionsnewyork.com

  13. #13
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: 50 amp 3 pole 4 wire service?

    Quote Originally Posted by Steven Turetsky View Post
    I never said that an equipment ground takes the place of a grounding electrode. I mentioned a few things that may be necessary, and also stated that His description wasn't too clear (to me).
    Sorry, that's the way it read in the line I quoted above.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •