Results 1 to 6 of 6

Thread: New one for me

  1. #1
    Join Date
    Mar 2007
    Location
    Knoxville, TN
    Posts
    2,560

    Default New one for me

    I have never seen this before. Someone removed one of the burners in a 50K gas furnace. The remaining burner was half covered in rust.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Orlando, FL
    Posts
    1,592

    Default Re: New one for me

    How did they seal the gas manifold?


  3. #3
    Join Date
    Aug 2008
    Location
    Pleasant Hill, Iowa
    Posts
    145

    Default Re: New one for me

    No reason to remove a burner unless it rusted out and they couldn't find one, looks like they sealed the manifold with an orffice plug. The pilot burner and thermocouple are still in tact and will lite the one atmospheric burner OK. The problem is condensation will build up on the left side and eventually rust through the heat exchanger. Depending on the age, the fan/limit switch needs to be on the right side to start the fan unless it is timed start from a circuit board, but then the limit switch also needs to be on the right side to protect for hi temp. Anytime someone removes a burner there are so many other factor that are involved in the operation and safety of the furnace. The burners can still be replaced and the heat exchanger cleaned unless it is too late. This needs to be put back to the original design cleaned and tested for CO, or the furnace needs to be replaced.

    Dan Hagman ACI
    ProSite Home Inspections
    Des Moines, Iowa

  4. #4
    Join Date
    Mar 2007
    Location
    Knoxville, TN
    Posts
    2,560

    Default Re: New one for me

    This unit is about 20 years old. They put a brass plug in the manifold. The one operating burner was half covered with rust. It was a mess.
    The house was a flip, and I told my client that the HVAC system really needed to be replaced.


  5. #5
    Join Date
    Mar 2011
    Location
    Pasadena, MD
    Posts
    13

    Default Re: New one for me

    Replacing a gas orifice with a plug was a common, but ill-advised method of derating a furnace back in the days of gravity vent furnaces. The recommended method was to reduce the orifice size on all the burners.

    In both cases, gas valves, burner baffles and flue baffles must be adjusted to prevent flue gas spillage, over-firing and to maintain an efficient gas flame. A combustion gas and flame analysis should be performed after each adjustment to confirm the burners are functioning efficiently.

    The presence of excessive rust could indicate the flue was too large and not baffled properly. This would cause slow draft resulting in excess condensation inside the flue pipe which would run back to the heat exchangers and burners causing premature rust.

    There are other possible causes for the rust. This is just a likely scenario due the presence of the plugged burner jet.


  6. #6
    Join Date
    Mar 2007
    Location
    Knoxville, TN
    Posts
    2,560

    Default Re: New one for me

    I think this one was rusted because its over 20 years old, and was not serviced for a long time. Since it was only a 50K unit to begin with, I'm thinking that taking out one burner is going to make it insufficient to heat the house come winter.

    I told my client that the HVAC system should probably be replaced.