    Sep 2008
    so so, California
    Default Need some help with this installation
    Need some help with this repair. Left vertical is a vent right is to a tub. I wasn't sure if there is a clearance between the San T and vertical drain? Educate me, thanks.
    Jul 2010
    New York
    Default Re: Need some help with this installation
    No problem with the clearance, but you have issues if the vent is supposed to be for the tub.
    Sep 2008
    so so, California
    my mistake, its not the tub...I'll re post when i remember what its for.
    IRC 3005.1 & 706 - the sanitary Tee on the left side of the picture is not supposed to be installed on its' back.
    Sep 2008
    so so, California
    thanks Markus.
    Correct, that sanitary tee should either be a wye and an eighth bend as installed at the bottom, or it could be a combination wye and eighth bend as either would go from horizontal to vertical.
    Jul 2010
    New York
    If left vertical is a vent as stated by OP, sanitary tee is allowed on its back as depicted. If left vertical is receiving discharge from any fixture, the tee would be incorrect.