    Default Need some help with this installation

    Need some help with this repair. Left vertical is a vent right is to a tub. I wasn't sure if there is a clearance between the San T and vertical drain? Educate me, thanks.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Jul 2010
    Location
    New York
    Posts
    30

    Default Re: Need some help with this installation

    No problem with the clearance, but you have issues if the vent is supposed to be for the tub.


  3. #3
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Need some help with this installation

    my mistake, its not the tub...I'll re post when i remember what its for.


  4. #4
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Need some help with this installation

    IRC 3005.1 & 706 - the sanitary Tee on the left side of the picture is not supposed to be installed on its' back.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  5. #5
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,867

    Default Re: Need some help with this installation

    thanks Markus.

    Last edited by Marc M; 10-05-2012 at 08:38 AM.

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Need some help with this installation

    Quote Originally Posted by Markus Keller View Post
    IRC 3005.1 & 706 - the sanitary Tee on the left side of the picture is not supposed to be installed on its' back.
    Correct, that sanitary tee should either be a wye and an eighth bend as installed at the bottom, or it could be a combination wye and eighth bend as either would go from horizontal to vertical.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Jul 2010
    Location
    New York
    Posts
    30

    Default Re: Need some help with this installation

    If left vertical is a vent as stated by OP, sanitary tee is allowed on its back as depicted. If left vertical is receiving discharge from any fixture, the tee would be incorrect.