    Can a double lug be installed in the main service entrance ground connection so at to extend to remote panel? (To avoid double tap)(one conductor under one screw)

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Mar 2012
    Location
    Ben Lomond, CA
    Posts
    72

    Default Re: extending neutral bus

    Is there no ground bus? Or is the problem fitting the wire into the bus (too large)? The main problem with a double lug, is if it appears as a splice to the inspector. The requirement is for a continuous, unspliced grounding electrode conductor from the grounding point (rod, pipe, rebar tie, etc.) to the main service termination point, usually a grounding bus marked for that purpose.


  3. #3
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: extending neutral bus

    Quote Originally Posted by Jose Quinones View Post
    Can a double lug be installed in the main service entrance ground connection so at to extend to remote panel? (To avoid double tap)(one conductor under one screw)
    Yes, there are auxiliary bars or lugs that are made for the purpose. This will likely need to come from an electrical supplier (not the big orange box store)