    Default single ground wire to bundle

    Does anyone see a problem with this?...It's a first for me..

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper
    Critical Home Inspection Services
    www.Home2Spec.com

  2. #2
    Join Date
    Mar 2007
    Location
    Myrtle Beach, South Carolina
    Posts
    341

    Default Re: single ground wire to bundle

    Thank you.

    Critical Home Inspection Services
    www.Home2Spec.com

  3. #3
    Join Date
    Mar 2009
    Location
    Colorado Front Range
    Posts
    684

    Default Re: single ground wire to bundle

    Victor, it can "reasonably" be expected that there is no current on a grounding conductor under normal circumstances. In the event of a fault it can "reasonably" be expected that the fault current will only be on one of the grounding conductors in the bundle that is crimped, so there is no reason why one grounding conductor of the largest present in the crimped bundle couldn't handle the largest expected fault current present in the bundle - and be the connection to the ground buss.

    Occam's eraser: The philosophical principle that even the simplest solution is bound to have something wrong with it.

  4. #4
    Join Date
    Apr 2008
    Location
    Western Massachusetts
    Posts
    536

    Default Re: single ground wire to bundle

    Still, all that nonsense for want of a $10 grounding bus bar. The shortcuts some people take...