    Default Need help with code reference

    Last edited by Jeff Eastman; 12-19-2007 at 03:09 PM.
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Houston, Texas
    Posts
    294

    Default Re: Need help with code reference

    M1501 of the IRC it states that the dryer exhaust piping is to terminate per the dryer manufacturer's specifications. I am quite certain the dryer manufacturer does not specify a B-vent termination cap for the end of the dryer exhaust system.

    Obviously that vent termination cap is not intended to be used to terminate a clothes dryer exhaust. That is a use inconsistent with its Listing and Labeling. There is also a presumption in the code that something like a Listed and labeled B-vent termination cap is going to be used for the purpose its manufacturer intended.



  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Need help with code reference

    I don't have time to look up the code, but it can't have a screen and it needs to have a baffle that allows it to close when it is not in use. Also as it is going out the roof you need to check the distance that it travels.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Need help with code reference

    Irc 2003 M1501.1
    Screens shall not be...
    Exhausts shall be equipped with a back draft damper.

    The back draft damper is in the hood.
    I doubt he wants to try to install a seperate damper.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Need help with code reference

    From the IRC.
    - M1502.2 Duct termination. Exhaust ducts shall terminate on the outside of the building. Exhaust duct terminations shall be in accordance with the dryer manufacturer’s installation instructions. Exhaust ducts shall terminate not less than 3 feet (914 mm) in any direction from openings into buildings. Exhaust duct terminations shall be equipped with a backdraft damper. Screens shall not be installed at the duct termination.

    When you look at the manufacturer's installation instructions, you will not see 'Type B Gas Vent Cap' listed as one of the options.

    Also, this from the IRC.
    - SECTION M1302
    - - APPROVAL
    - - - M1302.1 Listed and labeled.
    Appliances regulated by this code shall be listed and labeled for the application in which they are installed and used, unless otherwise approved in accordance with Section R104.11.

    Those are listed and labeled as Type B Gas Vent Caps, not 'dryer exhaust' caps.



    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Need help with code reference

    Quote Originally Posted by Warren Alderman View Post
    is it allowed to discharge a dryer vent onto the roof covering?
    Yes.

    You are not really discharging in "onto" the roof covering, you are discharging it "into" the air above the roof covering.

    It is done quite often and they make special dryer exhaust vent roof cap flashings for that. No screen, has a damper, and there is a neck down inside below the roof sheathing over which the dryer exhaust slips and is connected and sealed to.