Results 1 to 14 of 14
01-18-2013, 04:35 PM #1
Service entry neutral was #2 & Hot was 3/0
Inspected house today with service entry neutral cable a #2 and the hot ungrounded service entry cables were #3/0, this cant be correct ?
Does anyone know if this was allowed in 1973. TKS
Similar Threads:Last edited by Sam Morris; 01-18-2013 at 05:22 PM.
01-18-2013, 05:12 PM #2
01-18-2013, 05:17 PM #3
Re: Service entry neutral was #2 & Hot was 3/0
Decades ago the code specifically allowed the neutral to be two wire sizes smaller than the hot conductors. Now, however, the neutral conductors are required to be sized for their load, meaning that (typically) the neutral will be the same size as the hot conductors unless the electrical contractor shows load calculations to justify a smaller size neutral ... sometimes, the neutral conductor needs to be larger than the hot conductor due to harmonics, which can lead to increased current on the neutral.
01-18-2013, 05:20 PM #4
01-18-2013, 05:24 PM #5
01-18-2013, 05:26 PM #6
01-18-2013, 06:05 PM #7
For residential single phase services in my area the neutral is typically two sizes smaller. Pretty much all SEU and URD I can buy is like this from the factory. 4/0, 4/0, 2/0AL for 200A services, and 2,2,4AL for 100A.
4/0,4/0,4/0 & 2,2,2 are available, but not readily.
In this case however I can't think of any code that would have allowed it. Although, I was pretty young in '73.
01-18-2013, 09:26 PM #8
im just a lurker around here but:
Section 220.22 : the neutral demand load shall be the maximum unbalance computed load between the neutral and any one ungrounded conductor.
the neutral doesnt see the same loads as the hots.it doesnt see the load of the dryer or (to a extent) the stove or the hvac.that leaves you lighting and receptacles and what little you get from a stove neutral.so could of been smaller,at least in the past.
<a href=http://download.cnet.com/Free-Youtube-Downloader-Pro/3000-2071_4-75329731.html >youtube downloader</a>
01-20-2013, 08:14 AM #9
01-20-2013, 09:52 AM #10
01-20-2013, 12:09 PM #11
Robert,
Think of it this way - if the neutral was two sizes smaller than allowed for the overcurrent rating but the feeder hots were larger than necessary for the overcurrent rating, and someone were to install a higher overcurrent rating main to match the rating of the feeders - the neutral would now be woefully undersized.
01-20-2013, 04:23 PM #12
01-20-2013, 04:30 PM #13
Not as I recall the wording in the code. The wording in the code was, as I recall, that the neutral was allowed to be 'two sizes smaller than the ungrounded conductors', not that the neutral was allowed to be 'two sizes smaller than the required size of the ungrounded conductors' - makes a big difference with that different wording.
01-20-2013, 05:28 PM #14
True, I was watching football and did not pull out the books.