Results 1 to 35 of 35

Thread: Hot neutral bar

  1. #1
    Join Date
    Mar 2007
    Location
    Ft. Myers, FL
    Posts
    363

    Default Hot neutral bar

    Had a 1981 house today 200 AMP panel. Panel was full, lots of added circuits. Compressors, welders and an 80 AMP dock service. Would anyone agree that all the doubled and tripled neutrals together might have caused the neutral bar to get hot to the point of discoloring? The ground lug was also triple tapped.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral
    Paul Kondzich
    Ft. Myers, FL.

  2. #2
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Hot neutral bar

    No, I would not make that assumption.

    My first suspicion would be a loose connection at the big lug.
    But it would be best not to speculate at all and just say that amateur handiwork is suspected, list the faults, and call for repairs or replacement.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  3. #3
    Join Date
    Mar 2007
    Location
    Ft. Myers, FL
    Posts
    363

    Default Re: Hot neutral bar

    Quote Originally Posted by John Kogel View Post
    No, I would not make that assumption.

    My first suspicion would be a loose connection at the big lug.
    But it would be best not to speculate at all and just say that amateur handiwork is suspected, list the faults, and call for repairs or replacement.
    Thats what I did John, the question was more of a curiosity of mine. Thanks for the input.

    Paul Kondzich
    Ft. Myers, FL.

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Hot neutral bar

    The cause of that discoloration is that the neutral terminal is not securely attached to the neutral terminal bus (the lug is loos for some reason), OR, or the neutral conductor may be loose in the neutral terminal lug, or may have been loose in the neutral lug at one time and was subsequently corrected.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Hot neutral bar

    Quote Originally Posted by Paul Kondzich View Post
    Would anyone agree that all the doubled and tripled neutrals together might have caused the neutral bar to get hot to the point of discoloring?
    I have seen brand new panels still in the box have similar discoloration so I am guessing it may sometimes be caused by the manufacturing process.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  6. #6
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: Hot neutral bar

    Not a safe assumption. If neutrals were getting hot enough to discolor the bar, then I would expect to see melted and/or blackened insulation.

    If you choose not to decide, you still have made a choice.

  7. #7
    Join Date
    Mar 2012
    Location
    Michigan
    Posts
    43

    Default Re: Hot neutral bar

    A loose lug would be my guess from the color. I have heard the electricity traveling the wires in industrial plants immediately with a large draw. The wires move it seems. Over time they should be checked, especially when using industrial welders, as lugs can loosen if not properly torqued.

    Everything has its beauty but not everyone sees it.

  8. #8
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Hot neutral bar

    Quote Originally Posted by Jim Luttrall View Post
    I have seen brand new panels still in the box have similar discoloration so I am guessing it may sometimes be caused by the manufacturing process.
    This!


  9. #9
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Hot neutral bar

    Quote Originally Posted by Lon Henderson View Post
    Not a safe assumption. If neutrals were getting hot enough to discolor the bar, then I would expect to see melted and/or blackened insulation.
    AND this!

    That discoloration was NOT caused by heat.


  10. #10
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Hot neutral bar

    Quote Originally Posted by Speedy Petey View Post
    AND this!

    That discoloration was NOT caused by heat.
    The lug appears to be tarnished as well, but since you are never wrong, it must be a strange coincidence. Ignore it?

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  11. #11
    Join Date
    Mar 2012
    Location
    Michigan
    Posts
    43

    Default Re: Hot neutral bar

    It appears that the insulation is expanded, near the lug, to me. My paper ruler (yes I use one on the screen to prevent scratches) shows a size difference when compared to the neighbor wire, also a difference on the wire on the lug as it nears the termination point. This may be due to the depth perception phenomena, since they are so far away from each other.

    Everything has its beauty but not everyone sees it.

  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Hot neutral bar

    Quote Originally Posted by Speedy Petey View Post
    This!
    Quote Originally Posted by Speedy Petey View Post
    AND this!

    That discoloration was NOT caused by heat.
    Wow! You must know All the details related to that installation to be that sure of yourself.

    While I, too, have seen SIMILAR looking discoloration on new bus bars ... with SIMILAR ... being the key word, THE PATTERN of the discoloration suggests the cause was heat.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Hot neutral bar

    Quote Originally Posted by John Kogel View Post
    The lug appears to be tarnished as well, but since you are never wrong, it must be a strange coincidence. Ignore it?
    Why be a jerk? I wasn't.
    Why not wait for me to be a jerk then you can be a jerk back.


  14. #14
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Hot neutral bar

    Quote Originally Posted by Jerry Peck View Post
    Wow! You must know All the details related to that installation to be that sure of yourself.
    Yes I do. That is a pic of my own panel and I know ALL the details.



    Quote Originally Posted by Jerry Peck View Post
    While I, too, have seen SIMILAR looking discoloration on new bus bars ... with SIMILAR ... being the key word, THE PATTERN of the discoloration suggests the cause was heat.
    Jerry, you are usually more on top of these things than most here. I am surprised you see it this way.
    IMO and experience I see no signs of over heating in any of the pics shown.


  15. #15
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Hot neutral bar

    Quote Originally Posted by Richard Skalski View Post
    It appears that the insulation is expanded, near the lug, to me.
    I see that too, but also look at how distorted the rectangular lug is. I think it's distortion from the wide angle shot.


  16. #16
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Hot neutral bar

    Quote Originally Posted by Speedy Petey View Post
    Why be a jerk? I wasn't.
    Why not wait for me to be a jerk then you can be a jerk back.
    I knew you could handle it.

    Greener inspectors come here to learn. A scorched patch in a panel needs to be checked out.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  17. #17
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Hot neutral bar

    Quote Originally Posted by Speedy Petey View Post
    Yes I do. That is a pic of my own panel and I know ALL the details.


    Jerry, you are usually more on top of these things than most here. I am surprised you see it this way.
    IMO and experience I see no signs of over heating in any of the pics shown.
    Pete,

    I was/am referring to the photo in the original post ... NOT the photos you posted.

    The photo iusuallyhe original post shows discoloration on the top left corner of the terminal lug, and the discoloration on the neutral bus is greatest at, and appears to originate from under, that lug, the discoloration then spreads out and diminishes from there. There are also what look like could be arc marks below the terminal. All of which indicate to me that heat could be the cause.

    Pete, usually you pick up on those things and do not rush to judge the cause, thereby eliminating a viable cause in such an adamant manner.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  18. #18
    Join Date
    Mar 2011
    Location
    Virginia Beach, VA
    Posts
    123

    Default Re: Hot neutral bar

    Okay,

    Am I the only one going to question the stupidity of multiple Neutral conductors sharing positions on the bus bar?

    Every single one of those doubled up positions must be removed. Think about the increased load being carried by these Neutrals.

    Just suppose, the moron connects a 30 amp Neutral and a 15 amp Neutral into the same hole, what is going to happen?

    You are allowed to place multiple EGCs into the same hole, but not Neutrals.


  19. #19
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Hot neutral bar

    The doubled neutrals are not going to carry any more load than a single neutral. In the case of a #10 and a smaller conductor sharing a hole the smaller conductor might not receive the proper torque and be loose and heat up. The return current is not going into the other circuit. It is trying to get back to its source, the transformer.

    All answers based on unamended National Electrical codes.

  20. #20
    Join Date
    Mar 2011
    Location
    Virginia Beach, VA
    Posts
    123

    Default Re: Hot neutral bar

    We have agree to disagree with each other.

    How about this, with two Neutrals in the same hole you are sharing the Neutral with 2 or more breakers thus creating unbalanced multiwire branch circuits.

    Regardless, the placing of multiple Neutrals into the same hole on the Neutral Busbar is not allowed.

    Please refer to NEC 2008 - 408.41, than fail this panel board!

    Last edited by Donald Farrell; 01-13-2013 at 06:16 PM. Reason: left out NEC code reference

  21. #21
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Hot neutral bar

    The neutrals are not being shared any more than if they were in two holes in the bus. The current is not leaving one neutral and going into the other one.

    All answers based on unamended National Electrical codes.

  22. #22
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Hot neutral bar

    The multiple bonding conductors sharing the same terminal including different sizes and type (solid vs. stranded, awg).If drop check for a replacement bug on the N. Suspect a loss of same occured, possibly fault or overheating with close proximity (doesn't BELONG THERE) with unstripped NM cable sheath and paper insulation wrap in midst of grounded & bonding conductors to the R of bars (60C), durring a lightning arrestor or distribution breaker reset or the unexpected resumption of utility power while using an improperly transfered and improperly grounded generator hookup/decoupling 'event'; IOW an objectional current event (on the groundING not the groundED, "side".

    Note tracking to L of the bonding terminal - and see the inappropriately present white NM cable sheath and paper insulation to the right of same.
    You *might* find discoloration when/if the NM cable sheath inppropriately located, is examined and stripped for appropriate routing.



    The sharing of terminal, esp. this terminal, in this manner, is not correct. The smaller (undersized) solid copper conductor is neither stranded, compact stranded, nor is it of a size (too small) allowed for this terminal, and it is one of three in a terminal not rated to be shared with dissimilar conductors (dissimilar as to type - stranded vs. solid -- dissimilar does not just pertain to tinned copper vs. bare copper or copper vs. aluminum, etc.), and not for a conductor of its meager size, nor is it allowed to be shared in a terminal not rated for more than one conductor, and even if rated for two conductors, (certainly not three conductors, esp. one of dissimilar type) and would have to be so marked.

    Note the unterminated, uncovered ends, "clipped" cable to the right of the bars:



    Last edited by H.G. Watson, Sr.; 01-13-2013 at 08:32 PM.

  23. #23
    Join Date
    Mar 2011
    Location
    Virginia Beach, VA
    Posts
    123

    Default Re: Hot neutral bar

    Jim,

    Did you review NEC 2008 - 408.41 yet? If you want I can verify the sane citation in the 2011 edition of code

    When you clamp two wires together you are splicing them, just as if you capped them together. How difficult is that to understand? When one Neutral serves 2 breakers it is by definition a multiwire circuit.

    The correct way to fix this panel is to add additional Neutral busbars and make the proper connections.

    To not flag this panel is to just beg for a serious problem for an unsuspecting owner.


  24. #24
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Hot neutral bar

    You are not sharing the neutrals. They are simply terminating at the same bus in the panel. Using your analogy that the wires in the same hole are spliced, all the circuits in the panel are sharing a neutral due to the conductivity of the bus.

    All answers based on unamended National Electrical codes.

  25. #25
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Hot neutral bar

    Quote Originally Posted by Robert Meier View Post
    I agree, if the two neutrals in one hole are tight it's electrically no different than being in different holes. Although the NEC has a separate hole for each requirement.
    Thank you, I did not think it was hard to understand what I was saying.

    All answers based on unamended National Electrical codes.

  26. #26
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Hot neutral bar

    Quote Originally Posted by Jim Port View Post
    You are not sharing the neutrals. They are simply terminating at the same bus in the panel. Using your analogy that the wires in the same hole are spliced, all the circuits in the panel are sharing a neutral due to the conductivity of the bus.
    Jim,

    Just to clarify - you are not saying that having two neutrals in the same terminal is okay ... are you?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  27. #27
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Hot neutral bar

    Quote Originally Posted by Jerry Peck View Post
    Pete,

    I was/am referring to the photo in the original post ... NOT the photos you posted.

    The photo iusuallyhe original post shows discoloration on the top left corner of the terminal lug, and the discoloration on the neutral bus is greatest at, and appears to originate from under, that lug, the discoloration then spreads out and diminishes from there. There are also what look like could be arc marks below the terminal. All of which indicate to me that heat could be the cause.

    Pete, usually you pick up on those things and do not rush to judge the cause, thereby eliminating a viable cause in such an adamant manner.
    "Pete" didn't post any photos. The OP and later Robert Meier did.

    but since "usually you" DON'T "pick up on those things and do" "rush to judge"....


  28. #28
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Hot neutral bar

    Quote Originally Posted by H.G. Watson, Sr. View Post
    "Pete" didn't post any photos. The OP and later Robert Meier did.

    but since "usually you" DON'T "pick up on those things and do" "rush to judge"....
    Watson, as usual ...
    "
    since "usually you" DON'T "pick up on those things and do" "rush to judge"....
    '

    You apparently did not read this post from Pete:
    Quote Originally Posted by Speedy Petey View Post
    Yes I do. That is a pic of my own panel and I know ALL the details.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  29. #29
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Hot neutral bar

    Quote Originally Posted by Jerry Peck View Post
    Jim,

    Just to clarify - you are not saying that having two neutrals in the same terminal is okay ... are you?
    No I am not. I am disputing that they are now a shared neutral the way Donald sees it.

    All answers based on unamended National Electrical codes.

  30. #30
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Hot neutral bar

    Quote Originally Posted by Jim Port View Post
    No I am not.
    I didn't think you were, just wanted to make sure.

    I am disputing that they are now a shared neutral the way Donald sees it.
    I agree with you in what you are saying with regard to what Donald said, but I also suspect that Donald is not saying what he means to say, and I suspect that part of the problem is Donald using the term "shared neutral" and what that term means to us.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  31. #31
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Hot neutral bar

    Quote Originally Posted by Jerry Peck View Post
    Watson, as usual ...
    "
    since "usually you" DON'T "pick up on those things and do" "rush to judge"....
    '

    You apparently did not read this post from Pete:
    Actually, I DID.

    As usual, it is only YOU who quite obviously CAN NOT follow the FLOW of one of your many thread-hijacking side conversations!

    YOU challenged Pete's earlier statements made about "THAT" panel - (a statement made BEFORE Robert Meier posted ANY photos of a completely different panel). Pete sarcastically responded to your commentary "THAT" panel (that pictured in the OP, the one his first comments which you challenged, were made about) and his statements WERE regarding "THAT picture" to the Original Post panel pictures pictured, were/as his own.

    YOUR response

    Quote Originally Posted by Jerry Peck
    I was/am referring to the photo in the original post ... NOT the photos you posted
    Clearly shows it was YOU who were lost! Speedy Pete's commentary including the sarcastic remark regarding ownership was pertaining to THE PHOTOS in the ORIGINAL POST. Robert Meier's photos popped up (cross posting) in the MIDDLE of YOUR challenging interragories.

    Pete's subject "that picture" "that" "panel" (pictured in the OP) was established already - by Pete, and he was sarcastically responding and claiming ownership of was the Orignal Posted photos - YOU are the ONLY one who was "confused" as to the subject panel of his remarks, sarcastic response and otherwise.

    Last edited by H.G. Watson, Sr.; 01-20-2013 at 11:48 AM. Reason: format missing a bracket for quote to display properly.

  32. #32
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Hot neutral bar

    Quote Originally Posted by H.G. Watson, Sr. View Post
    ... in the MIDDLE of YOUR challenging interragories.
    Talk about describing yourself, sheesh!

    ... YOU are the ONLY one who was "confused" ...
    You are, as is typical for you, confused, argumentative, arrogant, and ... too many other obnoxious things to bother bending everyone's ear with here, we all see what you are like, and your posts only continue to confirm it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  33. #33
    Join Date
    Mar 2007
    Location
    Ft. Myers, FL
    Posts
    363

    Default Re: Hot neutral bar

    Wow, I had no idea my post created so many responses. I have my email set to notify at every response to post. I got the last one from Mr Watson who was not even the last response. In this case, the buyer supplied the electrician with a copy of my report. The electrician happens to be a friend of mine. He also assumed it was a loose main neutral lug and called the utility to pull the meter. This assumption was looking at the pictures not being on site. When the meter was pulled the main neutral lug was tight. The first four (top to bottom) neutral lugs were loose. He assumes that's where the discoloration came from. He also added he had never in 30 years seen that discoloration out of the box in regards to a panel.

    Paul Kondzich
    Ft. Myers, FL.

  34. #34
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: Hot neutral bar

    That's very interesting. Because the insulation on the wires isn't melted, it doesn't appear to me that heat is the source of the discoloration. I wonder if free electrons or radical molecules released by microshorting at the loose lugs caused the discoloration.

    If you choose not to decide, you still have made a choice.

  35. #35
    Robert Rolleston's Avatar
    Robert Rolleston Guest

    Default Re: Hot neutral bar

    I have seen a few times when I buy a panel that the bus has a rainbow like discolouration to it. Never though too much about it.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •