    I have never seen this before. No conventional trap present. Can anyone ID this?
    Norm
    Default Re: What is this ?
    Bottle trap
    Norm Peery's Avatar
    Norm Peery Guest
    Thanks, Rick
    Joe Funderburk's Avatar
    Joe Funderburk Guest
    P3201.5 Prohibited trap designs. The following types of
    traps are prohibited:
    1. Bell traps.
    2. Separate fixture traps with interior partitions, except
    those lavatory traps made of plastic, stainless steel or
    other corrosion-resistant material.
    3. “S” traps.
    4. Drum traps.
    5. Trap designs with moving parts.
    A trap is a simple U-shaped piping arrangement that
    offers minimal resistance to flow. Certain traps or arrangements
    are prohibited.
    Code commentary: ...
    Item 2 refers to separate fixture traps with interior
    partitions, except those lavatory traps made of plastic,
    stainless steel or other corrosion-resistant material.
    Such lavatory traps are sometimes referred to as bottle
    traps
    . This item refers to independent traps that are
    not integral with the fixture. For example, water closet
    traps are a form of partition trap, but because they are
    part of the fixture they are not prohibited. Partition
    traps are single-wall traps that rely on a single partition
    to separate the house side of the trap from the sewer
    side of the trap. Although they may be made of corrosion-
    resistant material, they are still subject to corrosion
    and can fail structurally. Because such failure
    does not result in leakage, there will be no indication of
    the lost trap seal.
    "P3201.1 Design of traps. Traps shall be of standard design,
    shall have smooth uniform internal waterways, shall be
    self-cleaning
    and shall not have interior partitions except
    where integral with the fixture. Traps shall be constructed of
    lead, cast iron, cast or drawn brass or approved plastic
    . Tubular
    brass traps shall be not less than No. 20 gage (0.8 mm) thickness.
    Solid connections, slip joints and couplings are permitted
    to be used on the trap inlet, trap outlet, or within the trap seal.
    Slip joints shall be accessible."
    A bottle trap is not self-cleaning and is prohibited by the IRC and IPC in my opinion.
    After seeing several in new homes and remodels.
    (Almost all pedestal sinks use a bottle trap, just about the only thing that will allow the close fit to the wall.)
    Anyhow, I asked the AHJ, and was told they (AHJ) do not disallow the use of bottle traps.
    Quote Originally Posted by Joe Funderburk View Post
    You do know what a lavatory is, right? (pictured).
    The partition trap is allowed, it is servicable as well.
    The outside cover finish appearance is no indication of what the material constituting the trap itself actually is INSIDE (most often plastic at the big box stores).
    You first quoted what actually ALLOWS this within the ordered list as an exception to what is prohibited. Granted its a specific permissive listed as an exception ("except those") to a generalized prohibition...but the model code language you first quoted permits a separate-from-the-fixture (not integral to the fixture) partition trap for a lavatory.
    You then quoted the commentary that further explained its (unammended) permissive use.
    made of plastic, stainless steel or other corrosion-resistant material.
    That's the problem as I see it. Service is not supposed to be required, as the code says it should be "self cleaning".
    P.S. You misspelled serviceable.
    (I added bold and italic to the quote below)
    1. Bell traps.
    3. ā€œSā€ traps.
    4. Drum traps.
    are prohibited.
    traps
    the lost trap seal
    Note that the code itself says not allowed ... except ... then the commentary explains that even those excepted by the code should not be allowed as they can fail with no visible signs of that failure as the failure is fully internal to the trap.