    Walked into this older panel....main disconnect 60amps/220v....older service conductors cut off and left to rot at the bottom.....double tapping....GFCI inoperative.....i think there is a fuse on the right upper corner....any other observations would help!

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2

    Default Re: Help on this older panel

    The conductors at the bottom have been cut off and the service entrance conductors from the meter are coming into a 2 pole 60 amp breaker at the top right. I could not tell the size of the conductors feeding the 60amp 2 pole breaker. I'm uploading a couple more images to get a better view...

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  3. #3
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: Help on this older panel

    very simple,
    save a life
    Panel requires replacement!
    Period
    why screw around with a bastardized piece of crap?


  4. #4
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Help on this older panel

    Missing a cable clamp in the bottom. Mr. Sparky didn't have a hex wrench for those cable lugs? Is that a #14 wire on the 20 amp breaker?

    There's plenty of fodder there for an electrician. Best fix is a replacement, I agree with Wayne on that one.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  5. #5
    Join Date
    Feb 2013
    Location
    FLORIDA
    Posts
    41

    Default Re: Help on this older panel

    1200 bucks...replace the panel..and you and your client will be ablle to sleep at night..