Thread: Pressure Cooker
    Default Pressure Cooker
    Oil fired hot water boiler. Do you think it's safe to say the pressure relief valve is defective?
    Default Re: Pressure Cooker
    Looks like about 46 psi. What is the rating on the relief valve?
    30 PSI.
    Is it a hot water or low pressure steam system?
    Hot water. It needs servicing.
    Southwest US
    Definately time to get it checked out but I think I have seen more non operational pressure gauges than relief valves.
    END GLOBAL WHINING
    You can attach your std. hose thread water pressure gauge at the boiler drain and compare with the tricator gauge. If the gauge is correct at 46 psi, then you have two problems: bad pressure relief valve and overfilling the system. If there is an automatic fill valve, then that valve may be defective or someone may have bypassed it.
    If the boiler pressure is where it should be then of course, the tricator gauge needs to be replaced.
    I would include a recommendation as a boiler plate to the effect annual inspection/ testing and replacement of pressure relief and TPR valves should be labeled on the appliance cabinet right next to the valve.
    If there is a diaphragm expansion tank, the tank needs an isolation valve so you can test the air pressure at the Schrader valve and compare with the static system pressure. If water spits out of the Schrader, the diaphragm is blown.
    Of course, always check the rating plate to ensure the PV is per mfrs specs. Tall buildings will require a 50 psi system.