Results 1 to 4 of 4
  1. #1
    Janet Sturm's Avatar
    Janet Sturm Guest

    Default Soot in new fireplace

    We have a gas fireplace that is less than 2 years old and every time we run it we have a large amount of soot build up. When we asked the company about it they said that it was "burning off impurities" and will stop when they have completely burned off.
    We have burned it for MANY hours and the soot never gets better. Could there possibly be another issue that is being overlooked?

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Knoxville, TN
    Posts
    2,560

    Default Re: Soot in new fireplace

    It sounds like the flame is not adjusted properly.


  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Soot in new fireplace

    Quote Originally Posted by Jack Feldmann View Post
    It sounds like the flame is not adjusted properly.
    Or the logs are not set properly and are impinging the flame which then cause the gas to not burn properly and cause the soot.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Janet Sturm's Avatar
    Janet Sturm Guest

    Thumbs up Re: Soot in new fireplace

    Scott,
    It worked, thank you! Your simple answer solved a 2 year old problem! I had the flame set high because they were telling me I needed to burn off the impurities! Thank you again!


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •