    Default Gas Meter

    Shouldn't this gas meter vent be extended to the outside of the enclosure? There was a small vent in the door, but it smelled of gas when I opened it. The other times that I have seen the meter enclosed, the vent was extended to the outside of the cabinet.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    Jim Robinson
    New Mexico, USA

  2. #2
    David Banks's Avatar
    David Banks Guest

    Default Re: Gas Meter

    NFPA 5.7.2.1 Gas Meter location. Gas meters shall be located in ventilated spaces readily accessible for examination, reading, replacement or necessary replacement.

    5.8.5.1 Line Gas Pressure Regulators.
    (1) An independent vent to the exterior of the building sized in accordance with the regulator manufacturer's instructions shall be provided where the location of a regulator is such that a ruptured diaphragm will cause a hazard.
    (2) The vent shall be designed to prevent the entry of water, insects or other foreign materials that could cause a blockage.

    Good place for spider webs in your pic.