Results 1 to 18 of 18
    Steven Lim's Avatar
    Steven Lim Guest
    Default minimum footing depth for patio cover
    Default Re: minimum footing depth for patio cover
    Quote Originally Posted by Steven Lim View Post
    Does anyone know the minimum footing depth for a patio cover in San Jose, CA?
    Thank you.
    Without knowing all the specifics see link http://www.sanjoseca.gov/DocumentCenter/View/977
    18 inches is the very minimum.
    Nov 2011
    Oregon, USA
    The IRC likes to see either a 12" minimum, or below the frost line (not an issue in CA). They also defer to the local AHJ, so that would be the best source for a definitive answer.
    Quote Originally Posted by BridgeMan View Post
    San Jose ( see link ) has an 18 inch Minimum.
    Nov 2011
    Oregon, USA
    The San Jose link furnished is for building foundations. I'm not sure a patio cover qualifies as "a building." But I'll bet the local AHJ would have the answer.
    Yes, the AHJ may have requirements like we have - if there is a footing present then it is presumed that the patio could be enclosed, therefore a full and proper footings is required.
    Don't recall the OP specifying geo tech specifics, SFH, nor attached vs. detached Patio Cover. If multi-family, commercial, etc. the following citations/quotations does/do not apply:
    Link to 2010 California Residential Code (with 2011 Amendments) clickable link: State
    Link to San Jose, CA Municipal Codes, Title 24 (clickable link, navigate within to Residential Code (24.09): American Legal Publishing - Online Library
    Note ordinances updated subsequent to a prior poster's document which refers to outdated state codes.
    From the San Jose Municipal Codes, Title 24:
    24.09.100 Adoption of technical provisions of California Residential Code.
    A. Except as otherwise provided for in this chapter, the California Residential Code, 2010 edition, including the appendices thereto, together with those omissions, amendments, exceptions and additions thereto as amended in Title 24 of the California Code of Regulations are approved and adopted, and are hereby incorporated in this chapter by reference and made a part hereof the same as if fully set forth herein.
    B. One copy of the CRC has been filed for use and examination of the public in the Office of the City Clerk of the City of San José.
    (Ord. 28838.)
    24.09.110 Portions of California Residential Code which are not approved, adopted or incorported by reference.
    A. The following portions of the "California Residential Code, 2010 edition," are not approved or adopted or incorporated in this chapter by reference, and shall not be deemed to be a part of this chapter nor a part of the residential code of the City of San José:
    1. Section 1.8.3
    2. Section 1.8.4
    3. Section 1.8.5
    4. Section 1.8.6
    5. Section 1.8.7
    6. Section 1.8.8
    7. Chapter 1, Division II
    B. The following appendices are adopted:
    1. Appendix E; Manufactured Housing Used as Dwelling (excluding Sections AE101 through AE 307).
    2. Appendix G; Swimming Pools, Spas and Hot Tubs.
    3. Appendix H; Patio Covers.
    4. Appendix K; Sound Transmission.
    From the California Residential Code, 2010 edition (Apendix H, from the link to same provided earlier - above):
    Section AH106 FOOTINGS
    AH106.1 General. In areas with a frostline depth of zero as specified in Table R301.2(1), a patio cover shall be permitted to be supported on a slab on grade without footings, provided the slab conforms to the provisions of Section R506 of this code, is not less than 3.5 inches (89 mm) thick and the columns do not support live and dead loads in excess of 750 pounds (3.34 kN) per column.
    Note from Chapter 4, 2010 CRC:
    R407.3 Structural requirements. The columns shall be restrained to prevent lateral displacement at the bottom end. Wood columns shall not be less in nominal size than 4 inches by 4 inches (102 mm by 102 mm). Steel columns shall not be less than 3-inch-diameter (76 mm) Schedule 40 pipe manufactured in accordance with ASTM A 53 Grade B or approved equivalent.)
    Also from the 2010 California Residential Code, Appendix H:
    SECTION AH102 DEFINITION (Patio Covers):
    Patio covers. One-story structures not exceeding 12 feet (3657 mm) in height. Enclosure walls shall be permitted to be of any configuration, provided the open or glazed area of the longer wall and one additional wall is equal to at least 65 percent of the area below a minimum of 6 feet 8 inches (2032 mm) of each wall, measured from the floor. Openings shall be permitted to be enclosed with (1) insect screening, (2) approved translucent or transparent plastic not more than 0.125 inch (3.2 mm) in thickness, (3) glass conforming to the provisions of Section R308, or (4) any combination of the foregoing.
    Back to the San Jose Muni Codes, TItle 24, Residential Code (24.09, from Link provided earlier above)::
    24.09.310 Findings.
    The amendment set forth in Parts 1 and 2 of this chapter is reasonably necessary because of the following local geological and topographical conditions:
    A. San José is within a very active seismic area.
    B. Gypsum wallboard and exterior Portland cement plaster have performed poorly during recent California seismic events.
    C. The shear values for gypsum wallboard and Portland cement stucco contained on the code are based on monodirectional testing.
    D. The limitation on the use of these systems as set forth in the amendment until cyclic loading testing are performed and evaluated is a more restrictive standard which will better prevent damage which can result from local conditions.
    (Ord. 28838.)
    24.09.320 Seismic Reinforcing (CRC Section R403.1.3)
    CRC Section 403.1.3 is amended to read as follows:
    R403.1.3 Seismic reinforcing. Concrete footings located in Seismic Design Categories D0, D1, D2, as established in Table R301.2 (1), shall have minimum reinforcement. Bottom reinforcement shall be located a minimum of 3 inches (76 mm) clear from the bottom of the footing.
    In Seismic Design Categories D0, D1 and D2 where a construction joint is created between a concrete footing and a stem wall, a minimum of one No.4 bar shall be installed at not more than 4 feet (1219 mm) on center. The vertical bar shall extend to 3 inches (76mm) clear of the bottom of the footing, have a standard hook and extend a minimum of 14 inches (357 mm) into the stem wall.
    In Seismic Design Categories D0, D1 and D2 where a grouted masonry stem wall is supported on a concrete footing and stem wall, a minimum of one No. 4 bar shall be installed at not more than 4 feet (1219mm) on center. The vertical bar shall extend to 3 inches (76 mm) clear of the bottom of the footing and have a standard hook.
    In Seismic Design Categories D0, D1 and D2 masonry stem walls without solid grout and vertical reinforcing are not permitted.
    (Ord. 28838.)
    24.09.330 Wall Bracing (CRC Section R602.10 Table 602.10.1.2(2)).
    CRC Section R602.10 Table R602.10.1.2(2) is mended to read as follows:
    See link provided above to muni code Title 24, link to Residential Code, scroll down to Chpter 24.09 subsection, if applicable.
    HTH
    Last edited by H.G. Watson, Sr.; 02-24-2013 at 04:27 PM. Reason: Formatting issues with quotations.
    Jan 2012
    Stamford, CT
    As others have mentioned, best is to ask the AHJ. Back when I was building in California, just up the road in Vallejo, the AHJ had us install 12x12 footings for a patio cover.
    Feb 2013
    NY
    As Watson depicted 0" for a patio -BUT if there is any anticipated use other than a patio in the future now is the time to accommodate that.
    Joe Funderburk's Avatar
    Joe Funderburk Guest
    No footings required for a patio, driveway, or sidewalk around here. That would be kinda silly.
    Quote Originally Posted by Joe Funderburk View Post
    Guessing you missed the "Cover" part of "Patio Cover".
    High wind areas/hurricane zones, and BTW there ARE some "D" zones EVEN in NC/SC. Depends on topography, geo, and seismic as well as frost/freeze lines in addition to the size, loads, & method of construction, detached, attached, etc.
    The OP (hailing from San Jose, California - i.e. an area known for significant SEISMIC activity) regarding Patio COVER was NOT SILLY, far from it. The OP also did not indicate if said "Patio" is a slab (could be paver bricks permiable/perk-able bedding, for example), nor if slab if is conforming.
    I did miss it. But if the "patio cover" is not a structural or permanent part of the house, then no footing would be warranted in my view.
    Footer for the support post/column for cover/roof.
    Garry is correct - even if the patio is "detached" from the house and the "patio cover" is not a structural or permanent part of the house, it is itself a "structure" by definition, it is also a "building" by definition, and a footing is required to the extent stated in the applicable code for that type/style of building/structure.
    If the "patio cover" was "attached" to the house, it would still require supporting posts at the two outboard corners, and, depending on the live loads, beam size between those two support posts, additional support posts may be required; each support post would require a footing designed in accordance with code requirements or by an engineer - which should also meet code requirements, but being an engineer and the fact that they sign and seal their plans, fuzzy stuff gets signed off, and if not fuzzy enough to trigger 'this just does not look right', it gets approved based on being signed and sealed by the engineer. That said, though, we find engineered drawings which do not match the requirements of those same engineered drawings - everyone makes errors at one time or another.
    Nov 2011
    Oregon, USA
    I agree that anyone can make mistakes. Does make me wonder, though--I wonder how many professional engineers signed off on and stamped their seals on the plans for "Galloping Gertie" over the Tacoma Narrows before construction started?
    In Maryland, depending on the county, the patio cover/roof columns require footers (usually) depending on the cover design and materials. If the patio is to be enclosed then the walls have to have footers. So, trying to use an existing slab can become a problem if you pull a permit that has walls in the original design. Attached to the house or not.
    Bottom left photo is a patio cover attached to the house. A structure by definition?
    http://www.google.com/url?sa=i&rct=j...62501522538493
    Yes. It is also a "building" by definition. However, being attached makes it not a separate structure/building, it makes it part of the structure/building it is attached to.
