    Default Vent clearances from window

    What are the required clearances for this vent. It is serving a gas fired wall mounted direct vent unit located just inside.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance
    Ken Amelin
    Cape Cod's Best Inspection Services
    www.midcapehomeinspection.com

  2. #2
    Join Date
    Jul 2008
    Location
    Chicago
    Posts
    263

    Default Re: Vent clearances from window

    Hmm ... are you sure that is direct vent, i.e., the appliance is getting combustion air from outside the house?

    If not it will need a 4' min. clearance from beneath and from the side of a window or house opening. NFPA 12.9.2

    Mike Lamb
    Inspection Connection, Inc.
    http://www.inspection2020.com/

  3. #3
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default Re: Vent clearances from window

    Quote Originally Posted by Mike Lamb View Post
    Hmm ... are you sure that is direct vent, i.e., the appliance is getting combustion air from outside the house?

    If not it will need a 4' min. clearance from beneath and from the side of a window or house opening. NFPA 12.9.2
    Mike,

    My error.

    It is a natural draft vent. It get's it air from inside the house and there is no power to the unit.

    - - - Updated - - -

    I see these a lot.

    I tell people that it is too close to the window as exhaust gases may enter the living space, but their answer is almost alwaysw the same: "DUH" hello mr. inspector. Do you really think the window will be open in mid-winter when they are using it??

    They make a good point.

    Ken Amelin
    Cape Cod's Best Inspection Services
    www.midcapehomeinspection.com

  4. #4
    Join Date
    Jul 2008
    Location
    Chicago
    Posts
    263

    Default Re: Vent clearances from window

    Quote Originally Posted by Ken Amelin View Post
    Mike,

    I tell people that it is too close to the window as exhaust gases may enter the living space, but their answer is almost alwaysw the same: "DUH" hello mr. inspector. Do you really think the window will be open in mid-winter when they are using it?? They make a good point.
    It's a point but not a good one. Adults and children can open or crack a window in winter for any number of reasons and it doesn't have to be a good reason. A house can easily be under negative pressure and suck CO fumes right in from that vent. Report it as wrong and hopefully Mr. DUH won't be dead wrong.

    12.9.2 A mechanical draft venting system of other than direct-vent type shall terminate at least 4 ft (1.2 m) below, 4 ft
    (1.2 m) horizontally from, or 1 ft (300 mm) above any door, operable window, or gravity air inlet into any building. The
    bottom of the vent terminal shall be located at least 12 in. (300 mm) above grade.

    Mike Lamb
    Inspection Connection, Inc.
    http://www.inspection2020.com/

  5. #5

    Default Re: Vent clearances from window

    It's always good to report it, CYA!!


  6. #6
    Scott Cook's Avatar
    Scott Cook Guest

    Default Re: Vent clearances from window

    Since it is Natural Draft, not mechanical, the termination would have to be 5' above the connection to the appliance for proper draft, and 2' higher than any portion of a building within a horizontal distance of 10 feet. That would put it above the roof. This is my understanding of IFGC 503.5.4.


  7. #7
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: Vent clearances from window

    Quote Originally Posted by Ken Amelin View Post
    I tell people that it is too close to the window as exhaust gases may enter the living space, but their answer is almost alwaysw the same: "DUH" hello mr. inspector. Do you really think the window will be open in mid-winter when they are using it?? They make a good point.
    During extended power outages you hear stories of CO poisoning because people run a generator in the garage or basement. I think it's important to try and anticipate people's lack of common sense. Even when a vent is more than 4 feet under a window I make a comment about it. I could not care less about what some code or spec says.

    Eric Barker, ACI
    Lake Barrington, IL

  8. #8
    Join Date
    Mar 2007
    Location
    Kalamazoo, MI
    Posts
    117

    Default Re: Vent clearances from window

    Also, it's funny to see a masonry chimney right next to the wall vent. You'd think the vent could have been somehow tied into one of the chimney flues rather than the way the installer did it???

    RJDalga
    http://homeanalysts.com
    Kalamazoo, MI

  9. #9
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: Vent clearances from window

    Guys, sorry to burst your bubbles but that has to be a direct vent. Not mechanical vent, not natural draft per se but a thermosyphoning direct vent. Natural vent cannot terminate out a sidewall. Look closely and you'll see a pipe inside of a pipe. That's a direct vent. DVs cannot share with a fireplace flue.


    As always, locate the make and model and that will take you to the listed instructions which is where you get your clearances. Probably just fine where it is.

    Keep the fire in the fireplace.

  10. #10
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Vent clearances from window

    A typical distance for a direct vent unit is 12 " from an openable window, but don't quote me. I opened a manual for a Robur gas wall heater and got the typical 12". 30 cm in Canada.



    A. clearance above grade, veranda, porch, deck,
    or balcony (12 inches (30 cm) minimum)
    (3)
    B. clearance to window or door that may be
    opened (12 inches (30 cm) minimum)
    (3)
    C. clearance to permanently closed window
    (minimum 12 inches (30 cm) recommended to
    prevent condensation on window)
    D. vertical clearance to ventilated soffit located
    above the terminal within a horizontal distance
    of 2 feet (60 cm) from the center–line of the
    terminal (18 inches (46 cm) minimum)
    E. clearance to unventilated soffit (12 inches (30
    cm) minimum clearance to vinyl soffit (36
    inches (90 cm) minimum)

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  11. #11
    Join Date
    Aug 2012
    Location
    Rock Hill S.C.
    Posts
    95

    Default Re: Vent clearances from window

    Quote Originally Posted by John Kogel View Post
    A typical distance for a direct vent unit is 12 " from an openable window, but don't quote me. I opened a manual for a Robur gas wall heater and got the typical 12". 30 cm in Canada.



    A. clearance above grade, veranda, porch, deck,
    or balcony (12 inches (30 cm) minimum)
    (3)
    B. clearance to window or door that may be
    opened (12 inches (30 cm) minimum)
    (3)
    C. clearance to permanently closed window
    (minimum 12 inches (30 cm) recommended to
    prevent condensation on window)
    D. vertical clearance to ventilated soffit located
    above the terminal within a horizontal distance
    of 2 feet (60 cm) from the center–line of the
    terminal (18 inches (46 cm) minimum)
    E. clearance to unventilated soffit (12 inches (30
    cm) minimum clearance to vinyl soffit (36
    inches (90 cm) minimum)
    Double 5 lap siding? 2" window sill? Anybody have a micrometer?


  12. #12
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Vent clearances from window

    Quote Originally Posted by Chris McIntyre View Post
    Double 5 lap siding? 2" window sill? Anybody have a micrometer?
    And do you measure to the flange or to the inner surface of the exhaust vent?

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  13. #13
    Join Date
    Jun 2010
    Location
    Rochester, NY
    Posts
    31

    Default Re: Vent clearances from window

    Lot of good replies.

    One additional thought, some of these devices are thermostatically operated, in which case the argument the window will be closed is a total fail unless the window automatically closes.

    A window open that low in the building envelope is likely to see negative pressure to indoors due to the buildings stack pressure.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •