Results 1 to 5 of 5
  1. #1
    Join Date
    Oct 2010
    Location
    Southwest US
    Posts
    585

    Default Large conductor taps

    I haven't run into these before. I am guessing they are OK as they appear to be manufactured for this and are stamped CU/AL.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance
    END GLOBAL WHINING

  2. #2
    Dennis Webber's Avatar
    Dennis Webber Guest

    Default Re: Large conductor taps

    Feeder taps are in article 240.21(B)(1) through (5).

    I've never seen anything like this, wonder if these taps were listed for this, or designed for ground conductors?

    Tap isn't on service side is it?


  3. #3
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Large conductor taps

    I don't see any images.

    All answers based on unamended National Electrical codes.

  4. #4
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Large conductor taps

    They are fine used within the proper size range of the conductors they are listed for. They can be used for grounded or ungrounded conductors.

    OCP would need to be provided at the remote end of the tap. The tap would also nned to meet the rules for taps.

    All answers based on unamended National Electrical codes.

  5. #5
    Join Date
    Oct 2009
    Location
    michigan
    Posts
    421

    Default Re: Large conductor taps

    I can't decern the size of the tap conductors but it appears that size requires a bushing on the connector (side). Yes, non metallic requires bushings also and have seen the damage done w/o.
    This type of tapping device is prone to issues especially with Al. if anti-oxhide compound is not used.
    Wire bending space and amount the conductors being bent may be an issue as well.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •