Results 1 to 2 of 2
  1. #1
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Stucco Stop Strip

    Does anyone have a good photo of a properly installed stucco stop strip above a shingle roof? I'm trying to find a good example for my reports. Here is the incorrect version of the location I'm talking about.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance
    Jim Robinson
    New Mexico, USA

  2. #2
    Join Date
    Mar 2007
    Location
    Succasunna NJ
    Posts
    577

    Default Re: Stucco Stop Strip

    The diagram shows a minimum of 1 inch above the roof; ASTM C-1063 7.11.5 requires a minimum of 2 inches.

    Darren www.aboutthehouseinspections.com
    'Whizzing & pasting & pooting through the day (Ronnie helping Kenny helping burn his poots away!) (FZ)

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •