    Default PVC to Cast Iron Waste Pipe

    This is a 2" PVC drain going into a 3" cast iron sanitary T with a 2" branch. I'm not sure if the connection is being made with caulk or mortar. Is it possible a neoprene compression donut is stuck in there?

    If not what are options for repair?


    054TT.JPG
    084WW.JPG

    Similar Threads:
    Inspection Referral
    Mike Lamb
    Inspection Connection, Inc.
    http://www.inspection2020.com/

  2. #2
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: PVC to Cast Iron Waste Pipe

    Looks like it is mortared into the old cleanout connection. Connection is designed to fail over time. Yes you could install a neoprene hub but a new cleanout needs to be added at the PVC pipe for servicing.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  3. #3
    Join Date
    Jul 2008
    Location
    Chicago
    Posts
    263

    Default Re: PVC to Cast Iron Waste Pipe

    Thanks. You are right. That's a clean-out access.

    Mike Lamb
    Inspection Connection, Inc.
    http://www.inspection2020.com/

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: PVC to Cast Iron Waste Pipe

    Quote Originally Posted by Mike Lamb View Post
    Thanks. You are right. That's a clean-out access.
    And a sanitary tee is required there for the PVC. A clean-out access *is not* suitable for that use.

    Obviously ... it "can" be done because you took a photo of it having been done, however, it is "not allowed" to be done - big different in those two words 'can' and 'allowed'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Nov 2007
    Location
    Chicago
    Posts
    548

    Default Re: PVC to Cast Iron Waste Pipe

    TITLE 77: PUBLIC HEALTH



    CHAPTER I: DEPARTMENT OF PUBLIC HEALTH
    SUBCHAPTER r: WATER AND SEWAGE
    PART 890 ILLINOIS PLUMBING CODE
    SECTION 890.420 PIPE CLEANOUTS



    Section 890.420 Pipe Cleanouts


    ....
    ....
    ....
    h) Cleanout Plugs. A cleanout shall not have a plumbing fixture installed in it or be used as a floor drain.

    TITLE 77: PUBLIC HEALTH
    CHAPTER I: DEPARTMENT OF PUBLIC HEALTH
    SUBCHAPTER r: WATER AND SEWAGE
    PART 890 ILLINOIS PLUMBING CODE
    SECTION 890.320 TYPES OF JOINTS



    Section 890.320 Types of Joints

    ....
    ...
    ..
    i) Cement Mortar Joints. Except for repairs, cement mortar joints are prohibited.


    Section 890.330 Special Joints

    ....
    ...
    ..
    g) Plastic Pipe to Non-Plastic Pipe Joints. Joints between plastic pipe and non-plastic pipe shall be made only by one of the following methods:

    ....

    2) Non-pressure piping - Drain Waste Vent (DWV)

    A) Caulked lead joints with caulked adaptors.

    B) No-hub soil pipe shielded couplings with approved adaptor having a raised bead.

    C) Compression type joints for hub and spigot cast iron pipe.

    D) Threaded adaptors.

    - - - Updated - - -

    The part about cement mortar joints has to do with clay sewer repairs. In the past clay sewers were all installed using oakum and cement.