Results 1 to 22 of 22
    Apr 2007
    WESTMINSTER CO
    Default WIRE NUT DOUBLE TAPPING BREAKERS
    GUYS
    is it ok to wire nut three circuits to one breaker and i know the top wire nut has upper size wire nutted with smaller gauge wire. wrote it up to have repaired by licensed electrician. think i made right call--but can ammend report not due till tomorrow.
    thjanks
    cvf
    Default Re: WIRE NUT DOUBLE TAPPING BREAKERS
    Unless there is AL mixed with copper under the wire nut and the breaker size is appropriate there is no issue.
    I would amend the report, unless there was a problem like those already posted.
    Apr 2007
    WESTMINSTER CO
    jack
    ok to have two different size wires nutted together ?
    cvf
    As long as the smallest or lowest rated wire is protected at its ampacity it is fine.
    Mar 2013
    Md and or PA
    GUYS
    thjanks
    cvf
    It is only one circuit - not three
    That is the easy way to correct multiple tapped breaker terminals - connect the two-three-or more conductors to one new conductor with a properly sized wire nut connector and that one new conductor is then attached to the breaker.
    Given the correct conditions stated above: i.e., the smallest conductor rating matches the breaker rating; rated for the proper wire sizes; etc.; then all is okay.
    Also as stated in a post above, that is just one circuit.
    Mbrooke's Avatar
    Mbrooke Guest
    As long as the breaker is sized to the smallest conductor and the load doesn't exceed the breaker's handle rating your ok.
    Apr 2007
    WESTMINSTER CO
    ok thanks all got my answer
    Quote Originally Posted by Mbrooke View Post
    Whoa! Just to clarify this because your post was right below the post below: the breaker size is *not* sized to fixture wires from any fixtures, the breaker is sized to the branch circuit conductor size/rating.
    Yes, it's very common to have #16 or #18 AWG conductors in a fixture whip spliced to #12 or #10 branch circuit conductors using wire nuts.
    Don't want someone to get the idea that the breaker needs to be sized to 16 AWG 18 AWG fixture wires.
    Holladay, UT
    When does wire nutting multiple conductors together become an issue? I see where there is multiple instances of this in same panel. Why would you ever need to add a new panel if you could just keep adding conductors to existing breakers. I am not an electrician and am trying to learn for my clients benefit. Thanks for any advice.
    http://acloserlookslc.com/
    Mar 2010
    conyers, ga
    Branch circuit wiring is rated for max distance for amperage of protection. Fixtures are rated differently and many times can utilize size smaller, very short distances so not much resistance, are designed and approved as such, etc. Circuit protection is more for the branch wiring in the structure to prevent overloading and causing fires, not so much for the protection of the device connected.
    Tom, the issue would be if someone tried to run too much off of the circuit. Simply having a splice does not mean there is too much load connected. The loading could be the same with a single conductor attached as multiples spliced at the panel. The usage determines the loads, not the number of wires. A branch circuit could go in multiple directions from a device or junction box anywhere in the circuit.
    Also certain circuits are required to be dedicated to certain areas and are not to be shared. Kitchen/dining receptacles, bathroom receptalces and laundry circuits are common ones.
    Quote Originally Posted by Mike Clarke View Post
    "You got some 'splainin' to do ... " Huh?
    No, the rating is not based on "max distance".
    If you have a fixture drawing 20 amps, you will not find #18 AWG conductors coming from it.
    That is what I said: "the breaker is sized to the branch circuit conductor size/rating"
    Mar 2013
    Md and or PA
    Fixture wires normally have differnt insulation and sometimes different conductor materials. That is taken into account when sizing those fixture leads at the factory.
    Fixture wires are also sized based on the load expected to be imposed upon them.
    Daniel Mack's Avatar
    Daniel Mack Guest
    jack
    cvf
    Wire nuts have a rating for how many of each AWG and in which combination the wires can be to comply with the listing for each size wire nut. This information is generally supplied on the packaging or the manufacturers web site.
    - - - Updated - - -
    Jan 2012
    Stamford, CT
    Tom, besides what others have mentioned, one case where wire nutting multiple conductors in a service panel becomes a problem is when the max fill of the junction box (service panel in this case) is exceeded. This is usually not a problem in most newer panels, but could be a problem in some older panels that don't have much excess space to begin with.
    Dec 2009
    Corinth MS
    Would that not be in violation of using the panel board for a junction box? I understand the concept of using wire nuts in the panel board to extend wires or using them to correct double tapped overcurrent devices, but three wires to one seems like it would be using the panel board as a junction. Just curious.
    Quote Originally Posted by Joe Hendrix View Post
    No, because you are only extending the conductors to the breakers.
    Oct 2011
    california
    write it up
    Quote Originally Posted by frazier jeffery View Post
    write it up
    What aspect are you talking about writing up? The splices are allowed as has been said already in this thread.
