Results 1 to 21 of 21
  1. #1

    Default Cracked veneer brick....repairable?

    We inspected a residential building that had multiple cracking on brick veneer. About 6 years old. Owners do no want brick replaced. What are the best options to repair these cracked bricks? Thanks,

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Cracked veneer brick....repairable?

    Not much can be done with the brick that will not show, a good mason can tuck point the areas but that is about all.

    The stucco looks to be more problematic than the brick. No joints at disimilar materials, no weep screed just in the small section I can see.

    Did you see any interior wall cracks in the home?

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: Cracked veneer brick....repairable?

    Quote Originally Posted by Scott Patterson View Post
    Not much can be done with the brick that will not show, a good mason can tuck point the areas but that is about all.

    The stucco looks to be more problematic than the brick. No joints at disimilar materials, no weep screed just in the small section I can see.

    Did you see any interior wall cracks in the home?
    Agree, the stucco looks like a bigger issue. Appears to be an improper transition to brick, too.

    If you choose not to decide, you still have made a choice.

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: Cracked veneer brick....repairable?

    Is that real veneer with a 1" air space, or is that adhered veneer which is adhered directly to the substrate behind it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Feb 2008
    Location
    New York
    Posts
    869

    Default Re: Cracked veneer brick....repairable?

    Quote Originally Posted by Roni Litmanovic View Post
    We inspected a residential building that had multiple cracking on brick veneer. About 6 years old. Owners do no want brick replaced. What are the best options to repair these cracked bricks? Thanks,
    Before you get into repair, are you comfortable that the wall is stable?

    When you say the owners don't want to replace the brick, I assume you mean all of the brick. You could remove/replace the damaged brick only. Other than that you could seal the cracks with some type of grout, but unless you open the cracks I don't believe simply grouting the existing cracks will last.

    As mentioned above, there may be more going on than just the brick.

    Steven Turetsky, UID #16000002314
    homeinspectionsnewyork.com
    eifsinspectionsnewyork.com

  6. #6
    Dominiclp's Avatar
    Dominiclp Guest

    Default Re: Cracked veneer brick....repairable?

    the crack in the brick runs through, into, the stucco. white staining radiating from the top of the brick under the soffit and dirt in the corner are indicative of water escaping in this area. there appears to be a change in plane where the cracks are in the brick. the cause of the cracking, and type of system ie brick masonry cavity wall [veneer] or brick veneer adhered to stucco - must be known before recommendations for the crack repair can be made. a wider shot of the area may be helpful

    - - - Updated - - -

    the crack in the brick runs through, into, the stucco. white staining radiating from the top of the brick under the soffit and dirt in the corner are indicative of water escaping in this area. there appears to be a change in plane where the cracks are in the brick. the cause of the cracking, and type of system ie brick masonry cavity wall [veneer] or brick veneer adhered to stucco - must be known before recommendations for the crack repair can be made. a wider shot of the area may be helpful


  7. #7
    Join Date
    Aug 2010
    Location
    BC Canada
    Posts
    368

    Default Re: Cracked veneer brick....repairable?

    Quote Originally Posted by Scott Patterson View Post
    Not much can be done with the brick that will not show, a good mason can tuck point the areas but that is about all.

    The stucco looks to be more problematic than the brick. No joints at disimilar materials, no weep screed just in the small section I can see.

    Did you see any interior wall cracks in the home?
    What Kind of transition joint is supposed to be between brick & stucco on this right way? is a drip screed needed on this overhang section?


  8. #8
    sanjeev supayia's Avatar
    sanjeev supayia Guest

    Default Re: Cracked veneer brick....repairable?

    Quote Originally Posted by Roni Litmanovic View Post
    We inspected a residential building that had multiple cracking on brick veneer. About 6 years old. Owners do no want brick replaced. What are the best options to repair these cracked bricks? Thanks,
    Replacing bricks cost lot of money.Repoint the only solution.
    SmartChoice Home And Mold Inspections
    Brampton Home Inspections Mississauga Home Inspector Toronto - Home


  9. #9
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Cracked veneer brick....repairable?

    Quote Originally Posted by Peter Louis View Post
    What Kind of transition joint is supposed to be between brick & stucco on this right way? is a drip screed needed on this overhang section?
    A book you should consider having on y our bookshelf....
    All about stucco

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  10. #10
    Join Date
    Aug 2010
    Location
    BC Canada
    Posts
    368

    Default Re: Cracked veneer brick....repairable?

    Quote Originally Posted by Scott Patterson View Post
    A book you should consider having on y our bookshelf....
    All about stucco

    Thanks Scott: do you have any pictures which can address this kind of joints? Can you post any?


  11. #11

    Default Re: Cracked veneer brick....repairable?

    There is no too much cracking on the interior of the building. However, there have been numerous water leak issues which I know have affected the brick veneer. I'm wondering if maybe a flexible, clear polyurethane can seal those cracks to extend their life somewhat....No weep screed found anywhere.


  12. #12

    Default Re: Cracked veneer brick....repairable?

    I believe that the veneer is directly installed on stucco. I do not think there is a drainage plane installed behind veneer. This guys want the building waterproofed and repainted but are not too happy about replacing bricks. Attached a few more pictures with more cracking and visible efflorescence. Water is for sure getting behind veneer. What is the best way to transition these materials? Very tropical weather....rains about 8 months out the year. panoramic view.jpgbrick veneer transition.jpgcracked edge.jpg


  13. #13
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: Cracked veneer brick....repairable?

    Sealing brick like you are talking about sounds like a formula for future disaster. Any water that finds its way behind the brick, and it eventually will, will not end well.

    If you choose not to decide, you still have made a choice.

  14. #14
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Cracked veneer brick....repairable?

    Engineering Study Required- improperly designed (lack thereof), executed & maintained structural building modifications, esp. to 4th/5th+ floor penthouse, (semi-?) occupied roof deck, penthouse overhang addition to balcony and balcony modifications to floors below, drainage, etc.

    Lipstick (seal coating) on a Pig (failing or corroding superstructure and veneer ties (steel corrosion expansion) alone will only make worse; failure to flash correctly, improper plane modifications, loading, failing H atop out-of-plane window opening at penthouse addition/enclosure at penthouse, etc. plus uplift & wind area.


  15. #15
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Cracked veneer brick....repairable?

    Quote Originally Posted by Peter Louis View Post
    Thanks Scott: do you have any pictures which can address this kind of joints? Can you post any?
    I'm sure I do, I just do not have the time to hunt for them. Sorry....

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  16. #16
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Cracked veneer brick....repairable?

    "About 6 years old"

    I do not believe the building ITSELF is merely 6 years old! Perhaps the conversion or modifications of issue are six years old.





    "believe that the veneer is directly installed on stucco"

    I seriously doubt that "belief".


  17. #17
    Join Date
    Feb 2008
    Location
    New York
    Posts
    869

    Default Re: Cracked veneer brick....repairable?

    Roni,

    You started out with a photo of a single location showing a few bricks and brick to stucco transition, and asked if the cracks could be repaired. Now we are looking at a high rise building with water intrusion and multiple symptoms. My best advice would be to bring in an expert Building Envelope specialist (expert is beyond certified) to survey and evaluate the entire system. Believing what may or may not be is not what that building needs. Everything you mentioned, plus more must be confirmed. Testing and sampling is necessary.

    I highly doubt that the owners of that building will remove the entire system and start over, even if that is the best answer. You may find yourself in a situation where alternative solutions may have to be considered. Since there may or may not be more than one contributing factor the task of remediation may be a process.

    Sometimes it is cheaper to go first class. Whatever the additional cost of the Building Envelope Inspection costs should save your clients exponentially what they will lose in wasted time, effort and money.

    By the way, sealing the system may be part of the final solution. And although compared to total removal and restoration may be a drop in the bucket, it is still not cheap. In my opinion to simply apply sealant on that building without remediation of certain areas will be a waste of time, effort and money.

    Last edited by Steven Turetsky; 04-30-2013 at 09:01 AM.
    Steven Turetsky, UID #16000002314
    homeinspectionsnewyork.com
    eifsinspectionsnewyork.com

  18. #18

    Default Re: Cracked veneer brick....repairable?

    Steven,

    Just to clarify, this building is a residential family building that is 8-9 stories high. It belongs to a family of brothers. Each floor is occupied by one of the members of the family. Anyway, what you see in the pictures is all original design. There have been no modifications whatsoever to the building siding or structure. I am attaching a picture of inside where you can see bricks behind cavity masonry wall drenched in water from a leaking pipe.

    Here where we are (Panama) there are no Expert Building Envelope Specialists. Just tons of architects and engineers. Anyone interested in coming down to tropical Panama to take a look at this? I can present proposal to owners and take it from there....

    What a disaster......

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  19. #19
    Join Date
    Feb 2008
    Location
    New York
    Posts
    869

    Default Re: Cracked veneer brick....repairable?

    Roni,
    I have PM'd you with some current information.

    Steven Turetsky, UID #16000002314
    homeinspectionsnewyork.com
    eifsinspectionsnewyork.com

  20. #20
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: Cracked veneer brick....repairable?

    Quote Originally Posted by Roni Litmanovic View Post
    I believe that the veneer is directly installed on stucco. I do not think there is a drainage plane installed behind veneer. This guys want the building waterproofed and repainted but are not too happy about replacing bricks. Attached a few more pictures with more cracking and visible efflorescence. Water is for sure getting behind veneer. What is the best way to transition these materials? Very tropical weather....rains about 8 months out the year. panoramic view.jpgbrick veneer transition.jpgcracked edge.jpg
    You should not suggest a repair. You need to understand the cause of the cracks and the type of construction before suggesting a repair. Its hard to tell from the photos, but it appears that corrosion of steel lintels or reinforcing steel in concrete may be a cause. They need further evaluation by a well qualified engineer or architect.


  21. #21
    Join Date
    Oct 2010
    Location
    MONTREAL QUEBEC-CANADA
    Posts
    2,075

    Default Re: Cracked veneer brick....repairable?

    The main brick veneer field looks in good condition.
    It appears the brick veneer under and beside the balconies are subject to moisture intrusion. It appears to be EFIS / Stucco.

    I concur with the other colleagues. A masonry company dedicated to this type of mixed veneer installation should be able to provide an qualified assessment. They usually have in-house engineers at the ready.

    Best of luck!

    Last edited by ROBERT YOUNG; 10-09-2015 at 07:25 AM.
    Robert Young's Montreal Home Inspection Services Inc.
    Call (514) 489-1887 or (514) 441-3732
    Our Motto; Putting information where you need it most, "In your hands.”

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •