05-13-2013, 12:49 PM #1
Emergency escape and rescue opening
Looking for comments and opinions on this setup. Its basically a double latched gate across a second story set of windows in a bedroom.
I am concerned because it requires some contortion to reach the latches and they both have to be manipulated simultaneously in order to get this contraption open. This just seems overly difficult to manage.
05-13-2013, 02:30 PM #2
Re: Emergency escape and rescue opening
Taken from IRC 1025.4
Operational constraints. Emergency escape and rescue openings shall be operational
from the inside of the room without the use of keys or tools. Bars, grilles, grates or
similar devices are permitted to be placed over emergency escape and rescue openings
provided the minimum net clear opening size complies with Section 1025.2 and such
devices shall be releasable or removable from the inside without the use of a key, tool or
force greater than that which is required for normal operation of the escape and rescue
opening. Where such bars, grilles, grates or similar devices are installed in existing
building, smoke alarms shall be installed in accordance with Section 907.2.10 regardless
of the valuation of the alteration.
05-13-2013, 06:43 PM #3
Fry Room 1. Fry Room 2 (if there are more than one)
Followed verbally with 'Would you like fries with that? - because that is what is going to happen'.