Results 1 to 15 of 15
Thread: stairway in garage
05-27-2013, 06:08 AM #1
stairway in garage
Homeowner remodeled house to put an upstairs room over the garage. The interior stairway passes through the garage. The underside of the stairway is exposed in the garage.
I'm trying to find good verbage for this: I was thining somethink like:
Underside of stairway which passes through the garage does not have a properly rated covering to provide the proper separation/fire rating between garage and living space.
05-27-2013, 07:25 AM #2
Re: stairway in garage
I would just say, "Stairway may lack required fire separation - check with AHJ" since it sounds like they should of had permits.
The way you have it worded sounds like you have the answer when they ask you, "What is the proper fire rating?" putting you in the position of Code Officer or Designer.
05-27-2013, 01:50 PM #3
Is the stairway open to the garage too?
If the stairway is enclosed (separated from the garage by at least 1/2{ gypsum board) then the stairway structure AND the walls AND the ceiling/floor of the garage/upstairs room IS REQUIRED to be protected by: at least 1/2" gypsum for the walls; at least 5/8" type x for the ceiling of the garage (which would also include the underside of the stairs as the underside of the stair would be 'ceiling').
The simplest way is to address the addition like this: Document that any additions, including the addition over the garage, were permitted, inspected, and received final approval and inspections. If the AHJ permitted it, inspected and, and approved it, then the presumption would be that it is in accordance with the code applicable within that AHJ.
05-27-2013, 01:56 PM #4
05-27-2013, 02:00 PM #5
05-27-2013, 02:24 PM #6
05-27-2013, 03:09 PM #7
05-27-2013, 03:34 PM #8
The underside of the staircase which is exposed in the garage would need to be covered with 5/8 inch type x sheetrock and properly taped/finished/sealed to provide a small window of time for egress in the event of a garage initiated fire. Properly sealed as well to reduce the chance of vehicle exhaust/fuel vapors from entering the home. Not to forget the need to be properly insulated now that this is an area between heated and non heated space and condensation formation can occur as well as a loss to the thermal envelope of the building. Jerry Peck nailed it with the 5/8 inch type x on the ceiling also as now there is a bedroom above. Now, also mentioned by another was an egress. Being that the bedroom is on the second level now another means of egress is needed via window/second stairs at exterior, etc.. Local code enforcement is not always up to par on this and even in major cities this requirement has been overlooked countless times. Good catch for your client....well worth the price of the inspection!!!!
05-27-2013, 04:51 PM #9
The entire staircase needs to be enclosed.
What is the upstairs room used for (not that it matters)?
05-27-2013, 05:06 PM #10
05-27-2013, 06:01 PM #11
Its a bedroom/bathroom.....with the balcony shown from my other post regarding EERO. The bedroom, bathroom, and stairway from the living room to the bedroom are not conditioned space. They have a window a/c in the upstairs bedroom. (POS home). what else should I expect? I live in the armpit of America...
05-28-2013, 05:22 PM #12
Staircase is open to garage.
Staircase leads to bedroom.
Bedroom (obviously) opens to staircase.
Bedroom (not so obviously, but I'm sure you got it) opens to garage ... and a bedroom is not allowed to open to a garage without an intervening space which separates (with doors) the bedroom and the garage - but you knew that, I was just connecting the dots for anyone who had not done so yet.
That is in addition to the fact that an egress path is not allowed to go through a garage (except in California, as I recall).
05-28-2013, 05:36 PM #13
Jerry, I think he was saying that just the framing of the stairs was exposed in the garage. Perhaps I misread somewhere. Wouldn't be the first time it happened and sure not to be the last time. With age come wisdom......wisdom to recognize our own flaws which increase with age. lol
05-28-2013, 06:44 PM #14
05-31-2013, 02:45 PM #15
Stairway to heaven if not gas/fire proofed.