Results 1 to 7 of 7
  1. #1
    Join Date
    Oct 2012
    Location
    Shelby NC
    Posts
    129

    Default How to deterine the proer size of return grill?

    How do I determine what is the proper size for a return grill. Usually I see 20x20 or multiple small grills. This house had a single that was about 10x16. Seemed small to me. Had low temp diffs too

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: How to deterine the proer size of return grill?

    Very general rule of thumb
    The return(s) should be larger than all the supply vents added together.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: How to deterine the proer size of return grill?

    Another very general rule of thumb - the returns should be larger than the return at the bottom of the air handler unit ...

    If not, yo' in fo' a heap o' troubl' ...

    This is what I do when set up like this: If air handler unit is an a closet with a louver return air (or louvered door), open the door part way and see if the door is sucked closed, if it is, open the door further, and further, and further ... until the door remains open - now measure the space from the edge of the door to the door casing, measure the height, measure the width of the door (the triangle space at the top, and at the bottom if the door is not close to the floor), add those areas up and that is how much more return air area the unit is trying to get - okay, rule of thumb as that does not take the static pressure designed and intended for the return into account, but it does make a lasting impression on the occupants when you open the door halfway, let the door go ... and the door slams itself shut! Yeah, there be a problem with that one.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Mar 2007
    Location
    Orlando, FL
    Posts
    1,592

    Default Re: How to deterine the proer size of return grill?

    Another "rule of thumb": If it was built before 2001, the return is too small.


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: How to deterine the proer size of return grill?

    Quote Originally Posted by Dom D'Agostino View Post
    Another "rule of thumb": If it was built before 2001, the return is too small.
    Dom,

    What changed in 2001 to make sure the return are still not too small?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: How to deterine the proer size of return grill?

    Quote Originally Posted by ren ramsey View Post
    How do I determine what is the proper size for a return grill. Usually I see 20x20 or multiple small grills. This house had a single that was about 10x16. Seemed small to me. Had low temp diffs too
    ACCA Manual D (second edition) recommends 300 fpm velocity at the face of the return grille. That edition if from the 1980s, but I don't think there have been significant changes in design since then. Use 400 cfm/ton for blower capacity. So a 3 ton system would need 4 square feet of total return grill area. The recommended velocity at the main return plenum is 600 fpm (700 max).


  7. #7
    Join Date
    Jul 2008
    Location
    Utah
    Posts
    390

    Default Re: How to deterine the proer size of return grill?

    Quote Originally Posted by Mark Reinmiller View Post
    ACCA Manual D (second edition) recommends 300 fpm velocity at the face of the return grille. That edition if from the 1980s, but I don't think there have been significant changes in design since then. Use 400 cfm/ton for blower capacity. So a 3 ton system would need 4 square feet of total return grill area. The recommended velocity at the main return plenum is 600 fpm (700 max).
    I agree with this and would add that a higher velocity would be acceptable but would start to generate noise above 400 FPM. Even at a higher velocity the system would (should) perform adequately.

    Good answer Mark.


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •