    Would the window need to be safety rated adjacent to this door? I say no because of the wall projection, but curious what you all think?

    Similar Threads:
    Last edited by brianmiller; 07-02-2013 at 03:52 PM.
    OREP Insurance

  2. #2
    Join Date
    Aug 2008
    Location
    Atlanta, GA
    Posts
    163

    Default Re: Safety glass needed?

    Quote Originally Posted by brianmiller View Post
    Would the window need to be safety rated adjacent to this door? I say no because of the wall projection, but curious what you all think?
    Hi Brian,

    The answer is "no" it is not required on that side. It would be required if that door was hinged on the left side and if the door swung towards the window where the nearest vertical edge of the window was with 24" of the arc of a door. IRC 308.4

    Some interpret the Code differently and I will see Tempered glass installed on this side too.


  3. #3
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Safety glass needed?

    From the 2006 IRC
    6. Glazing, in an individual fixed or operable panel adjacent
    to a door where the nearest vertical edge is within a
    24-inch (610 mm) arc of the door in a closed position
    and whose bottom edge is less than 60 inches (1524
    mm) above the floor or walking surface.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  4. #4
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: Safety glass needed?

    You may want to look at : page 3 of 5

    http://www.mybuildingpermit.com/Cons...et%2019_09.pdf

    If the window is within 24" of door and not 60" above floor.

    I know the argument will be that the door's hinged radius arc as installed is restricted to one side. The issue is that the door hinging can be changed. So Arc is relative to both sides of door jam.


  5. #5
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Safety glass needed?

    Garry, that's a good illustration.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  6. #6
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: Safety glass needed?

    Sometimes a picture/graphic sketch is worth a 1,000 words and two days of arguing over the meaning of "is".


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •