Results 1 to 6 of 6
  1. #1
    Join Date
    Aug 2007
    Location
    Bethlehem,Pa.
    Posts
    35

    Default Double Tapped Circuits

    Would like to know if you all call a double tapped circuit even if the one of the doubled up circuits is only going to a doorbell transformer.I have had a few electricians tell I'm not justified in making this call.

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: Double Tapped Circuits

    Quote Originally Posted by Eugene Cameline 3rd View Post
    even if the one of the doubled up circuits is only going to a doorbell transformer
    Eugene,

    It is not 'what' is multiple tapped off the terminal, it is that 'more than one' conductor is tapped off the terminal rated for 'one' conductor.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Double Tapped Circuits

    Quote Originally Posted by Eugene Cameline 3rd View Post
    Would like to know if you all call a double tapped circuit even if the one of the doubled up circuits is only going to a doorbell transformer.I have had a few electricians tell I'm not justified in making this call.
    As Jerry said, it makes no difference what it is powering. Brings up another point. I bet the transformer is laying in the bottom of the panel. This is wrong as well. You are not allowed to mix low and high voltage items in a panel like that.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: Double Tapped Circuits

    Ditto above two...

    The questions to be answered are;
    1) are the breakers rated for two conductors?
    and
    2) What kind of connection do you think is being make at the point of attachment? My point being that when you have two conductors under the same lug, more than likely there is a potential issue with the point of contacts for both conductors, if not rated for such an installation.

    rr


  5. #5
    Jack Ahern's Avatar
    Jack Ahern Guest

    Default Re: Double Tapped Circuits

    Door bell transformers --I see it so much (90%) that I write it up but do not discuss it. New homes--the AHJ must see it and pass ? on it. Door bell transformers are usually hung off of the (outside) the box. Go Sox and then Go Pats.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: Double Tapped Circuits

    Quote Originally Posted by Jack Ahern View Post
    Door bell transformers are usually hung off of the (outside) the box.
    Jack,

    That's okay (to be on the outside with the threaded fitting sticking in with the power conductors), but what Scott pointed out (transformer in the panel) is not.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •